i would track back along the pipes to see where the hot water stops my bet is a pair of ballofixes left under floor, half off,with some build up of dirt in them but that wouldnt explain the link pipe working ????
Ok guys.
The pipe to the rad does go over a wall and is horizontal for about 2 metres. I can't see the other side of the wall but I think it probably dips down so, yes, it could be an air-lock.
It doesn't "feel" like air though because when I drain from the return pipe, there is no spluttering and no air trapped in the rad.
I will still put in an automatic air vent, just in case.
I was going to put in full-bore iso valves so the flow would not be decreased.
If it was a blockage, I don't understand how the hot water is able to get thru if I drain some water from the return pipe. Surely a blockage would stop all flow?
It does seem to be a circulation problem because draining water from the return pipe encourages the water in the flow pipe and the rad will get hot and work for 2/3 days, until the water cools.( or until air builds up in the pipe ).
I just thought putting a small pump in the return pipe might be enough to keep the system working.
Thanks
i wouldnt bother with a pump, your far better solving the problem. you say you drag water through the return, have you also tried it with the flow?
blockage, if the blockage is in the flow of course you can get water out of the return as theres no blockage there
can you re connect the flow or return closer the boiler (not both) reverse return system
![]()
when hot it works when cold it doesnt. sound like a section is working on gravity and therefore the pump is missing the rad out as such. can you swap the tee for a swept tee
![]()