We have a Firebird oil boiler, 35kw and have recently started getting issues regarding condensate or lack of it. Long story as short as possible.
Boiler running without any issues for 2 plus years, unusual smell from it turns out to be plastic condensate trap melted. Looked into problem and it's common with Firebird so ordered and fitted new metal trap. Flap on air inlet pipe possibly stuck open at the same time so boiler burning too hot? released and check air flap, now all free and working well. Removed burner door and checked all plates and baffles seemed ok, very little soot so cleaned and re-fitted.
Primed trap before running.
All ok but then started hearing noise from condensate pipe when boiler fired up. Gurgling noise as air/gas passes through fluid in trap? Condensate runs to an external lift pump to take fluid out of cellar where boiler is fitted. There is a slight a smell now from boiler, sometimes, and have seen steam from end of condensate hose as it runs to condensate pump. Boiler working perfectly and efficiently but am concerned about fumes.
What might be making the steam / fumes exit boiler through condensate trap and pipe?
Boiler has been running at 60 - 65 degrees and I would assume that that means the return temperature is low enough to condensate and replenish fluid in trap. Flue outlet shows no sigh of smoke just normal smelling clean exhaust.
Any help or ideas much appreciated.
We are in France, as our badge shows, so burner was set up by Firebird to run on 35 sec fuel. No issues with boiler before the last couple of weeks.
Boiler running without any issues for 2 plus years, unusual smell from it turns out to be plastic condensate trap melted. Looked into problem and it's common with Firebird so ordered and fitted new metal trap. Flap on air inlet pipe possibly stuck open at the same time so boiler burning too hot? released and check air flap, now all free and working well. Removed burner door and checked all plates and baffles seemed ok, very little soot so cleaned and re-fitted.
Primed trap before running.
All ok but then started hearing noise from condensate pipe when boiler fired up. Gurgling noise as air/gas passes through fluid in trap? Condensate runs to an external lift pump to take fluid out of cellar where boiler is fitted. There is a slight a smell now from boiler, sometimes, and have seen steam from end of condensate hose as it runs to condensate pump. Boiler working perfectly and efficiently but am concerned about fumes.
What might be making the steam / fumes exit boiler through condensate trap and pipe?
Boiler has been running at 60 - 65 degrees and I would assume that that means the return temperature is low enough to condensate and replenish fluid in trap. Flue outlet shows no sigh of smoke just normal smelling clean exhaust.
Any help or ideas much appreciated.
We are in France, as our badge shows, so burner was set up by Firebird to run on 35 sec fuel. No issues with boiler before the last couple of weeks.