Hi,

I have just started a job where the system requires converting to a sealed system as customer wants to remove tanks from loft. I am just wondering where the expansion vessel is best fitted? Boiler is in garage so plenty of space. Does it need fitting on return? Never actually converted a system before so just a bit unsure! Also, how do i calculated the required size of expansion vessel? what size should i fit?
 
it is, its only a few year old glowworm ultacom hxi. Im confident doing the work, just not on sizing the vessel!
 
MI actually states to fit on flow near inlet of pump..
i have had this conversation on here and got accussed of not been competant because i asked the question should expansion go on flow or return,mi said flow but the return seemed to be favourable to most as for sizing there are sizing charts etc to use not to difficult
 
any downside to oversizing vessel? Reason i ask is because gloworm ultracom 2 sxi system boiler only has 8 litre expansion vessel in.
 
Last edited by a moderator:
It matters not a jot where it goes tbh.

My general rule of thumb though is always put it in the return or if it's going on the flow then id fit it between boiler and zone valves. Ie not after the zone valves on the flow

8litre does most 2/3 bed flats/houses, if it's quite a large house then I'd go for 12litre
 
Fitted on the return keeps the heat off it a bit and helps the diaphragm last a bit longer but it can be fitted on the flow or return doesn't make much odds.
 
Yea, fit it on return if possible - less heat & also recommended often by expansion vessel makers who usually say " on return, on suction side of pump & no valve to be put on pipe to vessel. " Also, some say to use an auto vent on pipe to vessel if it is on a high position, where air cannot get out.
Better the vessel is close to boiler & PRV should be at boiler always. Use the kit as has been said & that may make it simple, but the filling point can be anywhere handy on system, provided a pressure gauge is there too.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Converting to sealed system and expansion vessel vessel sizing" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
westyvip,
Last reply from
GQuigley67,
Replies
12
Views
9,026
Back
Top