Guest viewing is limited

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Dodgy Bypass Preventing Condensing

View the thread, titled "Dodgy Bypass Preventing Condensing" which is posted in UK Plumbers Forums on UK Plumbers Forums.

Screenshot_20181030-125425.png
IMG_20181030_112721.jpg

I am always surprised that Boilers don't display return temperatures. I manually adjust flow temps to achieve a return of about 53 as a form of weather compensation. Last time the best flow temp was 62 with return 54 and as you can see my solid walled home couldn't get there.

A hand on the return pre and post bypass showed the problem. Radiator returns were in the 40s. I estimate 50% of boiler flow was heading straight back. Interestingly the valve stayed jammed open even after the foreign body was out, presumably due to wear. It is a big aperture, so even a slight opening has a large curtain area.

Quick swap, Boiler temps now 70 - 50 and boiler output up from 10kw to 16kw.

I know this is not rare, but the lesson for me is to check return temps before and after the bypass regularly, when the system has recently started up.
 
View attachment 35187 View attachment 35189
I am always surprised that Boilers don't display return temperatures. I manually adjust flow temps to achieve a return of about 53 as a form of weather compensation. Last time the best flow temp was 62 with return 54 and as you can see my solid walled home couldn't get there.

A hand on the return pre and post bypass showed the problem. Radiator returns were in the 40s. I estimate 50% of boiler flow was heading straight back. Interestingly the valve stayed jammed open even after the foreign body was out, presumably due to wear. It is a big aperture, so even a slight opening has a large curtain area.

Quick swap, Boiler temps now 70 - 50 and boiler output up from 10kw to 16kw.

I know this is not rare, but the lesson for me is to check return temps before and after the bypass regularly, when the system has recently started up.
I love stuff like this , it’s very informative thank you
Rob Foster aka centralheatking
 
There is very little about this out there when I searched. So I posted this. I wondered how many boilers out there fail to condense for this reason, and how many are checked for this.

A man of great esteem and intellect such as Robert perhaps feels this stuff beneath them, their advice being to fit a leaky filter thingy I suppose.
 
View attachment 35187 View attachment 35189
I am always surprised that Boilers don't display return temperatures. I manually adjust flow temps to achieve a return of about 53 as a form of weather compensation. Last time the best flow temp was 62 with return 54 and as you can see my solid walled home couldn't get there.

A hand on the return pre and post bypass showed the problem. Radiator returns were in the 40s. I estimate 50% of boiler flow was heading straight back. Interestingly the valve stayed jammed open even after the foreign body was out, presumably due to wear. It is a big aperture, so even a slight opening has a large curtain area.

Quick swap, Boiler temps now 70 - 50 and boiler output up from 10kw to 16kw.

I know this is not rare, but the lesson for me is to check return temps before and after the bypass regularly, when the system has recently started up.
some do, good ones
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Dodgy Bypass Preventing Condensing" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
gpbeck,
Last reply from
dancinplumba,
Replies
3
Views
1,536
Back
Top