ian29gte
I have a four-circuit system, three for central heating, one for hot water, all on motorised valves, all thermostat controlled.
The top floor central heating is controlled by a Drayton Digistat wireless stat. With the central heating timer on, the circuit fails to operate, even though it shows green for heat, and the remote is calling for heat, with the flame symbol on. Batteries in the remote are OK, I've been through the set up cycle several times, and the lights do exactly what they're supposed to, but still no boiler lightup, and no motorised valve opening.
I believe the synchron motor is good, but will need to check, however there appears to be no power to it when the digistat light is green, calling for heat. I wonder if the wireless digistat box is duff, despite it showing the correct lights. Any help would be appreciated.
The top floor central heating is controlled by a Drayton Digistat wireless stat. With the central heating timer on, the circuit fails to operate, even though it shows green for heat, and the remote is calling for heat, with the flame symbol on. Batteries in the remote are OK, I've been through the set up cycle several times, and the lights do exactly what they're supposed to, but still no boiler lightup, and no motorised valve opening.