I think this may answer your question PIPE FITTING LOSSES
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
You can't do that! If you have a 20°C drop across the boiler you must also have a 20°C drop across the radiators.Yes, I know the drop is 20°C between flow and return at the boiler, however the 12°C drop was referring to across the radiator. I should have made that clear.
It's not really necessary to go into such detail. Most heating engineers (if they bothered to do the calculation) would use the standard number of 4.18 Joules per cc.First some values for water at 75 °C: Density 0.97486 g/cm³
Heat Capacity (per unit weight) 4.1927 J/g
Heat Capacity (per unit volume) 4.0873 J/cm³ (Density x Heat Capacity per unit weight)
In any case you are starting at the wrong end!
First you calculate the required boiler size using the Whole House Boiler Size Calculator. You then deduct 2kW (Domestic Hot Water Allowance) from the result to give the central heating requirement.
I'm not sure where you are including in the 10% loss.
You can't do that! If you have a 20°C drop across the boiler you must also have a 20°C drop across the radiators.
BS EN442 says that rad output has to be measured with a 10°C drop (...)
If a 20°C drop is used the radiator output will be reduced. You can see this if you compare the pages headed 50Δt and 40Δt in the Stelrad Elite Catalogue.
50Δt = (75+65)/2 - 20; [75-65=10]
40Δt = (70+50)/2 -20; [70-50=20]
Heat Capacity (per unit volume) 4.0873 J/cm³ (…)
It's not really necessary to go into such detail. Most heating engineers (if they bothered to do the calculation) would use the standard number of 4.18 Joules per cc.
So you did a heat loss calculation for each room and then compared the result with that obtained by using the whole house method? That's a "belt and braces" approach, but you gave the impression that you were just adding up the theoretical flows though each rad to obtain the boiler flow.No, I started at the right end, I have calculated my heat requirements and included 2kW. I found radiators closest to what I need and I think I have found a suitable boiler, I only needed to find out a few more things. That site (and some others) I've done and they confirm what I have calculated.
Don't understand what you are getting at. If your calculations show that you need a 20kW boiler, then you need one with an output of 20kW. Manufacturer's literature always show the output, so there's no need to assume a 10%loss.What it says on the box of a boiler is its maximum conversion of fuel (usually gas) to heat, not usable heat (hence the 90% performance combi boilers etc....).
Grandmothers and eggs comes to mind!Δt is comprised of Δ and t; t is temperature; Δ is the (ancient) Greek letter for delta and is used in maths as a symbol meaning difference. Thus 50Δt means a temperature difference of 50°C. With heating this is to indicate the difference between the temperature of the water in the radiator and air temperature. Rule of thumb air temperature will be room temperature of 20°C.
It is not nonsense! They are the temperatures used when testing radiators to BS EN442. This states that the flow temperature must be 75C, the return temperature 65C and the room temperature 20C (so that's not just "rule of thumb"). The mean water temperature is therefore 70C or (65+75)/2 and the mean difference between the radiator and the room is 70-20 or 50C, generally referred to as a 50C delta.This makes your equation 50Δt =(75+65)/2 – 20 nonsense.(75+65)/2 – 20 = 50, not a difference of 50, what you have there is an equation with randomly selected numbers, because they 'fit'.
Which catalogue are you referring to?Hi Doitmyself,
Again all with due respect, but you don't understand what the catalogue actually describes. And everything you say just seems to confirm you don't know the theory behind it.
I didn't know you were an expert on this topic!I just don't want to write another 'essay' explaining why you are wrong here.