hi chris, i understand what you are saying, thanks for the info. Just been again, as only next door. The expansion vessel was initial pressure setting of 0.5bar, (not 1.5bar like i commented before) tested vessel by pressurizing and pushing up the scrader valve, no waqter present so presume diaphragm is ok. The vessel is Tee,d off the gravity circuit for the hot water to coil. Heating side is of course pumped. Plenty of DHW so circuit is obviously flowing ( no restrictions in flow or return to boiler) There is a tub under the vessel to gauge the water lost, it was overflowing so a good 40 litres must of come out and the pressure gauge was reading approx 2.8bar ! still high with preesure and water lost !
I think we can eliminate blockages in pipework, or air locks. full heating system has never worked so well, very hot rads throughout and good hot water at cylinder.
Boiler is downstairs and cylinder is up stairs so average of 2.4metre to plus height to top of upstairs rads maybe 1metre. The longest run is the biggest "??" there are four bedrooms then a bathroom in a row so pipework must be 20 - 25metres plus another 10metre angled off this then down to the boiler.
the boiler itself is only on a low setting so its not overheating and boiling the water, the boiler has never clicked out, so not a temp issue, (apart from rate of expansion)
Im leaning toward a bigger tank, and playing around with the pressures, just a costly excercise if doesent cure it.