I have several baxi solos on yearly service contracts I have noticed lately they have occasional noisey boardering on explosion ingnition this is not all the time? these are stripped and cleaned out heat ex electrodes, ceramic burner hoovered all mi checks done and within acceptable limits , opinions chaps ? wondering if the ceramic burners wear over time ?? Not cheap to replace so looking for more info 🙂 . Cheers kop
 

Attachments

  • 20160204_135607.jpg
    20160204_135607.jpg
    266.6 KB · Views: 23
  • 20171109_143327.jpg
    20171109_143327.jpg
    565.7 KB · Views: 24
Found it, read it, been moderated.
Desperate to know now what the issue was.
 
Gas valve passing gas when it should be closed allowing a slight build up call for heat boom . Kop
 
I'd have guessed gas valve from here!
Was hoping for something interesting

I've had a mini spate of dodgy gas valves recently, 2 ideals and a vaillant in a fortnight?
 
  • Informative
Reactions: king of pipes
What is the normal pre purge time before ignition/gas valve opening on domestic boilers?.
 