I have to run the condensate external on two jobs.
this one has a 4m drop then a 3m horizontal run to termination so I was thinking
21.5 mm from the boiler to the floor to 32mm street elbow pointing up with a Tee and access plug pointing up so in the event it freezes you can pour a kettle in it. 32mm through the wall and down, two 45's to make a long radius bend to keep the flow and then to the drain. does that sound alright or should I put it up to 40 mm ?
the second job is going external to a stack but they have had a few blockages in the past.
should I run the 32mm into a 40mm elbow to give myself an air break ?
welcome to throw whichever object you wish.
gas man his axe....croppie his wallet....
I have to run the condensate external on two jobs.
this one has a 4m drop then a 3m horizontal run to termination so I was thinking
21.5 mm from the boiler to the floor to 32mm street elbow pointing up with a Tee and access plug pointing up so in the event it freezes you can pour a kettle in it. 32mm through the wall and down, two 45's to make a long radius bend to keep the flow and then to the drain. does that sound alright or should I put it up to 40 mm ?