Today I have had my internal soil stack removed and a new one fitted externally.

The soil pipe ends below my bathroom window with what i think is a durco valve fitted.

Several people have stated this does not meet building regs

2 questions

1) Is it within regulations to terminate the pipe below a window

2) using the durco valve, doesn't this stop the release of gasses. I though the idea was to allow free flow of gasses out of the top
 

Attachments

  • 20170321_192729.jpg
    20170321_192729.jpg
    88.8 KB · Views: 115
  • 20170321_192737.jpg
    20170321_192737.jpg
    90.8 KB · Views: 60
did you get permission to change the out look of the property? you might not need it!
not suposed to use durgo valve outside as the jam with dust.
vent stack is not above toilet bowl either!
 
toiletValve.jpg

the basin waste is not far enough away from the pan branch >200mm.
the top of the durgo should be min 100mm above opening window. (but there not recomended for outside as they jam open).
 
So you recommend taking the pipe above the window with an open vent in the soil pipe?

Thank you for your help.
 
So you recommend taking the pipe above the window with an open vent in the soil pipe?

Thank you for your help.
 
no, you need a meter above window opening without durgo.
its not installed correctly either way, typical builders own regs with picture teaching and no theory lessons!
soil stack changing comes under planning consent too from internal to external, but you might get away with it unless your selling up soon!
 
Sorry lads, but you can use a durgo externally. It must be rated for outside use, so it won't freeze in winter. Even though a natural vent is better, as it lets the drain vent both directions.
There might be a good reason why it hasn't been taken throgh, or offset round the soffit. But as a minimum it should have been tight under the eaves.
Must have been short of pipe, or a good ladder :sosp:
 
Sorry lads, but you can use a durgo externally. It must be rated for outside use, so it won't freeze in winter. Even though a natural vent is better, as it lets the drain vent both directions.
There might be a good reason why it hasn't been taken throgh, or offset round the soffit. But as a minimum it should have been tight under the eaves.
Must have been short of pipe, or a good ladder :sosp:
 
Sorry lads, but you can use a durgo externally. It must be rated for outside use, so it won't freeze in winter. Even though a natural vent is better, as it lets the drain vent both directions.
There might be a good reason why it hasn't been taken throgh, or offset round the soffit. But as a minimum it should have been tight under the eaves.
Must have been short of pipe, or a good ladder :sosp:

i know but it advises not to be used externally as they freeze or eventually jamb with dust and need exchanging! job half done imo.
 
i know but it advises not to be used externally as they freeze or eventually jamb with dust and need exchanging! job half done imo.

I agree, always best to run a propper vent to atmosphere. But the answer is, you can use a durgo outside.
 
i know but it advises not to be used externally as they freeze or eventually jamb with dust and need exchanging! job half done imo.

I agree, always best to run a propper vent to atmosphere. But the answer is, you can use a durgo outside.
 
Building Regulations Part H (2015) still states the following -
1.33 Ventilated discharge stacks may be terminated inside a building when fitted with air admittance valves complying with BS EN 12380:2002. Where these valves are used they should not adversely affect the amount of ventilation necessary for the below ground system which is normally provided by open stacks of the sanitary pipework. Air admittance valves should be located in areas which have adequate ventilation, should be accessible for maintenance and should be removable to give access for clearance of blockages. Air admittance valves should not be used outside buildings or in dust laden atmospheres. Where there is no open ventilation on a drainage system or through connected drains, alternative arrangements to relieve positive pressures should be considered.
Page 10 of H1
 