Hi, Does anyone know, what is the minimum distance between two 90 bends on flue system.

Can any one spot any problem other then no sufficient support, seal and flue terminal sticking out more than 100mm?

Any Help will be grateful.

Many Thanks

 

Attachments

  • 1.jpg
  • 3.jpg
  • 2.jpg
  • 4.jpg
  • 5.jpg
Last edited by a moderator:
is the flue terminal 300mm from any openings, dont think there is any minimum distance between 90 bends as long as there is enough flue to fit in the bends plus a couple of mm extra
 
Last edited by a moderator:
well yes it is more then 300, I would say around 600mm from the window.
 
deffo not right, i would say id + r

too close to an opening
too close to gutters
passing through a wooden fascia, with no protection
most manufacturers state it should only protrude from the building a certain distance typically 100mm - definetly exceeded ( possibly to try to avoid all the above issues - but breaking manufacturers installation instructions )


have fun with that one

shaun
 
No it was less then 300mm from the doorway as far as guttering concern it was well below 75mm as maintained in manufacture. Instructions, But still I think POC can be enter into property and that is why I would say “At Risk”.

Finally removed the existing flue and installed vertical Flue.

Bang on “both gas regs and Manufacture Instruction compiled


Thanks
 
No it was less then 300mm from the doorway as far as guttering concern it was well below 75mm as maintained in manufacture. Instructions, But still I think POC can be enter into property and that is why I would say “At Risk”.

Finally removed the existing flue and installed vertical Flue.

Bang on “both gas regs and Manufacture Instruction compiled


Thanks

did you sort that condensate out too? 22mm freezes every winter where i live. i wake on a icy morning and just wait for my phone to ring! lol....... oh yeah i'm not talking about my own i'm a stand in manager..
 