So our filling loop only seems to allow water to flow when you open it for about 3-5 seconds and then nothing. Trying to top up boiler pressure as it's about 0.7 bar. If you wait 5 minutes you can open filling loop and you get another 3-5 seconds of water through it before nothing happens again. Anyone help diagnose? Could it mean the boiler is full and the pressure gauge incorrect? Or could there be air in the system making the filling loop cut out after a few seconds of water flow?
 
Yes it could be that the boiler is full and electronic gauge is faulty. What make/model of boiler? Any photo of loop install?
 
Manual gauge could be blocked at the end then. They’re only thin copper, and the size of a large pinhole. If you’re under BG contract, you could get them out?
 
It's an old Ideal boiler about 20 years old I think - analogue pressure gauge. Filling loop renewed by BG only 2 years ago.
[/QUOTE

Unlikely, but maybe only 0.7/0.8 mains pressure available, possibly PRV if installed in filling loop needs increasing or maybe two vales on filling loop but only opening one?
 
Where is the boiler located? Height wise from the street? Have you enough pressure to go above what you’re currently getting?
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Filling loop issue?" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

Joined
Location
Surrey
Member Type
DIY or Homeowner

Thread Information

Title
Filling loop issue?
Prefix
N/A
Forum
Central Heating Forum
Start date
Last reply date
Replies
9

Thread Tags

Tags Tags
filling

Thread statistics

Created
Hawkmoon,
Last reply from
Timmy D,
Replies
9
Views
2,667

Weekly or Monthly Email Digest

Back
Top