BS5410 does not specify any longitudinal dimension for the position of the fire valve, except height, unless I'v missed it and you can point it out?
9.3.9 Where the sensitive element is positioned external to the appliance it should be located at a maximum height of 500 mm above the top of the burner.
All true, but I can't find anything in the legislation that stipulates the valve has to be a certain distance from the boiler.
Best, don't want to start an argument, but the Building Regulations Part J are UK Government legislation approved by the Secretary of State, OFTEC recommendations are not, however in Part J under "What is an approved Document" there is a paragraph which says:
"There is therefore no obligation to adopt any particular solution contained in this Approved Document if you would prefer to meet the relevant requirement in some other way. However, persons intending to carry out building work should always check with their Building Control Body, either the local authority or an approved inspector, that their proposals comply with building regulations."
Without an approved Government "Code of Practice" I assume industry guidance would be acceptable, but this is a decision that would have to be made by a Judge/Queens Council in a case requiring this decision to be made.
It would seem that as in most work place legislation if a COP is not available a self appointed body has become the voice of the industry and what they have published has become the work standard adopted/accepted.
Fire services after a house fire check for cause of fire and anything that had contributed to it. They will find out the oil hose had burnt through and greatly fuelled the fire without any proper isolation. Their report could be damning to last man at boiler.
All very true, but IMO a distance of 1M is not going to stop a fire serious enough to involve loss adjusters, from overtaking a fire valve and allowing the tank contents to empty.
Firstly, I would condemn the install as it presently is, just to keep myself right. So I would do as you and fit an internal firevalve as a minimum if customer agrees plus do the paperwork showing all the faults.How would you best deal with both an old boiler and steel oil tank in the garage. Boiler front is literally 1.5 mtrs from the tank. To improve situation I have installed a remote acting fire valve between boiler and tank. Outside wall is the boundary? I suggested when tank changed to install the fire valve outside, but client is wanting to put a Tuffa 60min fire rated tank back in the garage. ? Where do you put the fire valve?
What if outside wall is the boundry, which would mean you cant loop fire valve outside on someone elses property.Firstly, I would condemn the install as it presently is, just to keep myself right. So I would do as you and fit an internal firevalve as a minimum if customer agrees plus do the paperwork showing all the faults.
Probably best the remote firevalve is fitted on outside wall, even though it means looping out and back through wall.
No outdoor space for an oil tank?
No outside walls to their own property? Not a lot you can do then I guess. Would be interesting to know what OFTEC or building control would recommend.What if outside wall is the boundry, which would mean you cant loop fire valve outside on someone elses property.
I have failed tank as not compliant and insufficient fire protection. They could find a place outside, but have been told by oil supplier too far from drive. (plus 50mtrs?).
Tuff say they do a fire rated tank that can be installed in garage. I don't install tanks so advised he seek suggestions from tank installer.
Its the garage, front is open doors, one side is a lounge wall other two walls is neighbours garden.No outside walls to their own property? Not a lot you can do then I guess. Would be interesting to know what OFTEC or building control would recommend.
Oil suppliers my area I think do have capability to supply to oil tanks 100metres fill hose, although most I have seen would need much less distance