nutty_jah

Gas Engineer
Wonder if I could have some pointers with this boiler.

Flow switch is not being pushed out, with pump running. Pump rotation is strong (checked through the bleed screw), also taken out to check impeller which is securely attached.

When switch manually activated boiler kettles.

When flow and return valves isolated, pump pushes out rod to activate switch. Boiler obviously kettles.

I'm thinking it is a block main hex, any pointers? Thanks in advance. Nuran
 
Thanks guys, im back there on Monday so will check dhex and diaghpram.

@jtsplumbing. Yes it's a hard water area.

Now re dhex and split diaghpram. Dhex isn't in play is it if CH is called for. Unless div is stuck and trying to push through dhex.

And the diaghpram, suppose could be a split. Hence only activating when increased pressure when flow return closed.

Still doesn't explain the kettling when with pump running and switch manually activated.
 
Thanks guys, im back there on Monday so will check dhex and diaghpram.

@jtsplumbing. Yes it's a hard water area.

Now re dhex and split diaghpram. Dhex isn't in play is it if CH is called for. Unless div is stuck and trying to push through dhex.

And the diaghpram, suppose could be a split. Hence only activating when increased pressure when flow return closed.

Still doesn't explain the kettling when with pump running and switch manually activated.

either ch diaphragm has split ,the small one at the back,or the hole under its blocked get one of these in advance,you also need a stubby slot driver and a 8mm spanner Baxi Combi 105HE Central Heating Diaphragm Kit 5111138 NEW
 
Have you checked the filter on the return and the primary thermistor on the flow pipe from heat ex which is a wet pocket some times cap can get caught at this point
 
Have you checked the filter on the return and the primary thermistor on the flow pipe from heat ex which is a wet pocket some times cap can get caught at this point

have a gander at the post above yours, all fixed
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Flow switch not activating Baxi Combi 80Eco" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
nutty_jah,
Last reply from
lame plumber,
Replies
9
Views
239
Back
Top