samwilko

Gas Engineer
I went out to do a landlord safety check to day on an 8 year old property. There is a valiant ecotec 831 plus in the kitchen with only 220mm to the openable window.
There is a row of three of these houses all with the same flue too close to the kitchen window. All have passed every inspection up till now.
i phoned Vaillant just to double check i was t missing something here and for some reason this was allowed, you doubt yourself when everyone else has passed it and its been built so recently. They confirmed that it definitely needs to be 300mm away.
So i phoned gas safe just to double double check my self before causing any upset. I was shocked at the response I got.
I was convinced this was At Risk. window open, wind in right direction fault on boiler and hey presto carbon monoxide coming back into the kitchen.
According to gas safe though it is only non compliant. It would have been NCS when that existed but now its just non compliant and is not to be written on the CP12. He said I should just have a verbal conversation with the owner and that will suffice.
That is an absolute joke, how am I supposed to cover myself and make the tenant and landlord aware of the risk? By having a verbal conversation? I thought this was absolutely disgraceful, they are telling me to sign this off as safe according to the CP12.
 
quote; I was convinced this was At Risk. window open, wind in right direction fault on boiler and hey presto carbon monoxide coming back into the kitchen.

80mm not going to kill anyone though!

i think it should be a score system left to engineer.. 5=fekin dangerous-3= not right-1 its naff!
3 naffs and its sh1te
 
Wouldn't lose sleep over it. Lot worse out there. As long as co detector in house and all working ok just note that you mentioned it. Not saying it's right but demo won't cause any danger so can't be at risk.
 
Sure it says in the regs its only AR "if following an assesment POC are found to be entering the property"... See quite a few that are under 300mm think you just need to use your own judgment
 
Because it's diluted with outside air. Let's face it there's a potential with 300mm all depends on the wind direction.

its not fitted right but as wattsie says theres a potential even potential for CO to enter at 300mm given the right conditions. i wouldnt be losing sleep for 80mm just right it down on the sheet then your covered.
 
Take a picture, make note in your diary and right in the names of who you spoke to. Also anything else that will cover you.
 
There is no at risk for flue too close to an opening. It was either ncs or if poc entering property then id. It's written in black and white in the unsafe sits book.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Flue too close to the window, gas safe not interested." which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

samwilko

Gas Engineer
Joined
Location
Cornwall

Thread Information

Title
Flue too close to the window, gas safe not interested.
Prefix
N/A
Forum
Gas Engineers Forum
Start date
Last reply date
Replies
15

Thread statistics

Created
samwilko,
Last reply from
bewsh,
Replies
15
Views
562

Weekly or Monthly Email Digest

Back
Top