revising for my gas, trying to understand pipe sizing.

I've got the spec college book and I'm trying to get my head round the gas pipe sizing from the books from class. we don't start it until march but I'm wanting to get a head start as theres lot to study and I'm a slow learner.

I'm struggling with understanding the maximum pressure loss from the meter at any point of use is 1mb. can someone explain this in a easier way if they can.

also from the diagram i have with meter A to the first tee B is pipe length 3 meters long and states it has two elbows? overall equivalent length is 4meters. as the elbows at as 0.5 x 2.

i can't work out where the 2 elbows are? cause from B - C is a fire.

i hope this isn't too much for some ones advice.
 
Re: revising for my gas, trying to understand pipe sizing.

Maximum pressure loss from meter to each appliance is 1mbar

Lets say house Has a boiler
The maximum pressure loss from the meter to the boiler can only be 1mbar (the pressure is lost when the pipe is too small or theres too many bends)
 
Re: revising for my gas, trying to understand pipe sizing.

a---------------b------------------d
|
|
|
c
 
Re: revising for my gas, trying to understand pipe sizing.

if you can imagine below the b is the pipe work for c
 
Re: revising for my gas, trying to understand pipe sizing.

a-b i don't understand why it says there is 2 elbows? i lost.
 
Re: revising for my gas, trying to understand pipe sizing.

what about the 1mb maximum drop from the meter?
 
Re: revising for my gas, trying to understand pipe sizing.

can you explain about the pressure loss. i can find out the amount of gas required from the table but where it becomes a struggle to understand is when it talks about the maximum pressure loss at 1mb
 
Re: revising for my gas, trying to understand pipe sizing.

I've moved this to the arms because we don't discuss gas in open forum but at the same time we want to encourage and help you with your learning.

What the exercise is trying to do is get you to size each section of pipework so no section has a drop greater than 1mbar. I aim for 0.5 max but that's me.

The exercise shows you leg a-b, b-c and b-d with the appliance load on each leg. Because the diagram would be complicated by showing each bend and tee you're just told how many there are.

So, work out your size using m3/hr for leg b-c. Same again for b-d. Add your two loads together in m3/hr and work out your pipe size for a-b.

And then Bob's your aunt's live in lover.
 
[MENTION][MENTION][MENTION]
PHP:
[PHP][ATTACH]26787.vB[/ATTACH]
[/PHP][/MENTION][/MENTION][/MENTION]can someone find the answers for my pipe sizingIMG_1783.JPG
 
Last edited:

Official Sponsors of Plumbers Talk

Reply to the thread, titled "gas pipe sizing" which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

Inverness

Plumber
Gas Engineer
Plumbers Arms member
Joined
Member Type
General Plumber

Thread Information

Title
gas pipe sizing
Prefix
N/A
Forum
Gas Engineers Forum
Start date
Last reply date
Replies
65

Thread Tags

Thread statistics

Created
Inverness,
Last reply from
spanner,
Replies
65
Views
1,289

Weekly or Monthly Email Digest

Back
Top