Table B13 Gauges and their Limitations
[TABLE="class: MsoTableGrid"]
[TR]
[TD]
[/TD]
[TD="width: 120"]
[/TD]
[TD="width: 120"]
Typical Readable Movement
[/TD]
[TD="width: 117"]
[/TD]
[/TR]
[TR]
[TD="width: 211"]
Water (SG 1.0)[/TD]
[TD="width: 120"] 0 – 120[/TD]
[TD="width: 120"] 0.5[/TD]
[TD="width: 117"]
[/TD]
[/TR]
[TR]
[TD="width: 211"]
High SG (SG 1.99)[/TD]
[TD="width: 120"] 0 – 200[/TD]
[TD="width: 120"] 1[/TD]
[TD="width: 117"]
[/TD]
[/TR]
[TR]
[TD="width: 211"]
Electronic (1 decimal place)[/TD]
[TD="width: 120"] 0 – 200[/TD]
[TD="width: 120"] 0.5[/TD]
[TD="width: 117"]
[/TD]
[/TR]
[TR]
[TD="width: 211"]
Electronic (2 decimal places)[/TD]
[TD="width: 120"] 0 – 200[/TD]
[TD="width: 120"] 0.1[/TD]
[TD="width: 117"]
[/TD]
[/TR]
[TR]
[TD="width: 211"]
Electronic (1 decimal place)[/TD]
[TD="width: 120"] 0 – 2,000[/TD]
[TD="width: 120"] 0.5[/TD]
[TD="width: 117"]
[/TD]
[/TR]
[TR]
[TD="width: 211"]
Electronic (No decimal place)[/TD]
[TD="width: 120"] 0 – 20,000[/TD]
[TD="width: 120"] 5[/TD]
[TD="width: 117"]
[/TD]
[/TR]
[TR]
[TD="width: 211"]
Mercury (SG 13.5)[/TD]
[TD="width: 120"] 0 – 1,000[/TD]
[TD="width: 120"] 7[/TD]
[TD="width: 117"]
[/TD]
[/TR]
[/TABLE]
Always Ensure TTD is Less Than or Equal to the Maximum Permitted Time for the Gauge being used. Should TTD exceed the Maximum Permitted Time then the installation will have to be divided into sections and tested separately.
Table B14 Factor F1 using Fuel Gas at OP
[TABLE="class: MsoTableGrid"]
[TR]
[TD]
[/TD]
[TD="width: 192"]
[/TD]
[/TR]
[TR]
[TD="width: 199"]
Natural Gas[/TD]
[TD="width: 192"]
[/TD]
[/TR]
[TR]
[TD="width: 199"]
Butane[/TD]
[TD="width: 192"]
[/TD]
[/TR]
[TR]
[TD="width: 199"]
Propane[/TD]
[TD="width: 192"]
[/TD]
[/TR]
[/TABLE]
Table B16Factor F3
[TABLE="class: MsoTableGrid"]
[TR]
[TD]
Fuel Gas at OP (all gases)[/TD]
[TD="width: 192"]
[/TD]
[/TR]
[/TABLE]
[FONT=&]
[/FONT] Table B17 MPLR for different locations
[TABLE="class: MsoTableGrid"]
[TR]
[TD]
[/TD]
[TD="width: 426, colspan: 3"]
MPLR (m[SUP]3[/SUP] h[SUP]-1[/SUP] (st))
[/TD]
[/TR]
[TR]
[TD="width: 426, colspan: 3"]
[/TD]
[/TR]
[TR]
[TD="width: 142"]
Inadequately ventilated areas
(Area Type A)[/TD]
[TD="width: 142"]
Adequately ventilated internal area volume <60m[SUP]3[/SUP][/TD]
[TD="width: 142"]
Adequately ventilated internal area. Volume >60m[SUP]3[/SUP].
External, exposed or buried.
(Area Type C and D)[/TD]
[/TR]
[TR]
[TD="width: 142"]
Rate per m[SUP]3[/SUP] of smallest space volume
(Area Type B)[/TD]
[/TR]
[TR]
[TD="width: 142"]
Natural Gas[/TD]
[TD="width: 142"] 0.0014[/TD]
[TD="width: 142"] 0.0005[/TD]
[TD="width: 142"] 0.03[/TD]
[/TR]
[TR]
[TD="width: 142"]
Butane[/TD]
[TD="width: 142"] 0.00044[/TD]
[TD="width: 142"] 0.00016[/TD]
[TD="width: 142"] 0.0098[/TD]
[/TR]
[TR]
[TD="width: 142"]
Propane[/TD]
[TD="width: 142"] 0.00057[/TD]
[TD="width: 142"] 0.0002[/TD]
[TD="width: 142"] 0.0123[/TD]
[/TR]
[/TABLE]
Table B18 Formulae
[TABLE="class: MsoTableGrid"]
[TR]
[TD][/TD]
[TD="width: 179"]
ALL NEW, AND EXISTING IN AREA TYPE A
[/TD]
[TD="width: 167, colspan: 3"]
[/TD]
[TD="width: 164"]
[/TD]
[/TR]
[TR]
[TD="width: 58"]
TTD
(mins)[/TD]
[TD="width: 179"]
[/TD]
[TD="width: 22"][/TD]
[TD="width: 129"]
[/TD]
[TD="width: 16"][/TD]
[TD="width: 164"]
[/TD]
[/TR]
[TR]
[TD="width: 22"][/TD]
[TD="width: 129"]
[/TD]
[TD="width: 16"][/TD]
[/TR]
[/TABLE]
Table 18a Meter Volumes
[TABLE="class: MsoTableGrid"]
[TR]
[TD]
[/TD]
[TD="width: 417"]
Installation Volume, IVm (m[SUP]3[/SUP])
[/TD]
[/TR]
[TR]
[TD="width: 151"]
[/TD]
[TD="width: 417"]
[/TD]
[/TR]
[TR]
[TD="width: 151"]
[/TD]
[TD="width: 417"]
[/TD]
[/TR]
[TR]
[TD="width: 151"]
[/TD]
[TD="width: 417"]
[/TD]
[/TR]
[TR]
[TD="width: 151"]
[/TD]
[TD="width: 417"]
[/TD]
[/TR]
[TR]
[TD="width: 151"]
[/TD]
[TD="width: 417"]
[/TD]
[/TR]
[TR]
[TD="width: 151"]
[/TD]
[TD="width: 417"]
[/TD]
[/TR]
[TR]
[TD="width: 151"]
[/TD]
[TD="width: 417"]
[/TD]
[/TR]
[TR]
[TD="width: 151"]
[/TD]
[TD="width: 417"]
0.79 x d[SUP]2[/SUP] x L
[/TD]
[/TR]
[TR]
[TD="width: 151"]
[/TD]
[TD="width: 417"]
[/TD]
[/TR]
[/TABLE]
(Note: Number designates maximum volume of gas per hour through meter, e.g. U65 allows 65m[SUP]3[/SUP]/hr)
Calculation for Maximum Permitted Leak Rate in m[SUP]3[/SUP].
F3 x GM[SUB]corr[/SUB]x IVt
TTD
Where GM[SUB]corr[/SUB]is TTP at start of TTD minus TTP at end of TTD e.g.
TTP start 21.03mbar
TTP end 20.57mbar
GM[SUB]corr[/SUB] 0.46mbar