Hi apologies of this has been asked before but when you gas rate an appliance and trying to compare to the technical data, do you go off the Domestic hot water input as that’s a higher figure than the central heating max? Thanks
F9707567-103D-4A4A-ABB1-166A7B65660F.jpeg
 
I was always told all hot taps for maximum gas rate, or follow the mi’s for gas rating (will be in the servicing section).
 
You need to run at as high as you can get it by whatever means. e.g. on a Vaillant you would set it to P1 to run at Max rate, either on heating or DHW.
Using DHW will allow a continuous run so long as the flow rate allows the boiler to lose enough heat.
 
Thanks for the reply! Yeah I went out and did a vaillant the other day, stuck it on p1 and then 100 for max. But when I was trying to do the gas rate at the meter the boiler stopped firing up halfway through doing it?
 
If it’s up to 91 degrees, or there about, it will stop, and start again once temp dropped. Next time try P1, running the dhw tap and turning the room stat to max, it might work, it might not. If you’ve a partially blocked heat exchanger then it’ll get to temperature quicker and take longer to cool down.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Gas rating an appliance" which is posted in Gas Engineers Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

Joined
Location
Stourport
Member Type
Other Plumber

Thread Information

Title
Gas rating an appliance
Prefix
N/A
Forum
Gas Engineers Forum
Start date
Last reply date
Replies
6

Thread Tags

Tags Tags
gas engineer

Thread statistics

Created
jordyrusty,
Last reply from
Deleted member 120897,
Replies
6
Views
1,075

Weekly or Monthly Email Digest

Back
Top