P
philip134
Glow worm 60ff
4073A mid position valve seemed to be sticking. Delivering CH when only HW was called. Loosened spindle, replaced activator head, lots of clicking noises from head.
Now boiler doesn't fire. No lights on any of Neons 1 to 4. L to N inside box has 240v. N to SL has 0v. Connected L to SL - boiler fires, all 4 neons lit, pump runs.
Does this suggest that 4073A head is at fault? or pcb is at fault? Can I check some voltages on wires from activator head to help in sorting the problem?