Hi all, i got a kantankerous boiler that simply will not work. IE NO spark!
Fan runs,
pressure switch activates (i can hear it click)
but no spark.
followed fault finding and changed PCB at cost of 180£
but still no spark??????
I check resistence across soleniods and they both fall just within tolerance limites. 2.1 & 2.3 while min is 2.0KOhms.
with boiler on I checked voltage across pins on the gas solenoid but there was no 240v. Fault finding chart says replace PCB but i did that qalready!!!!
acording to manual the normal lighting sequence is so
1- the fan runs - check
2- the air pressure switch operates - check
3- the first pilot solenoid valve opens -
4- the sprak igniter operates
5- pilot lights
6- ignition spark switches off
7- second solenoid opens giving main burner operation
from what i read the gas solenoid must work in order for spark to commence but board is not sending 240 to solenoid...
this has left me confused so any help guys is really appreacited
cheers
DD368
Fan runs,
pressure switch activates (i can hear it click)
but no spark.
followed fault finding and changed PCB at cost of 180£
but still no spark??????
I check resistence across soleniods and they both fall just within tolerance limites. 2.1 & 2.3 while min is 2.0KOhms.
with boiler on I checked voltage across pins on the gas solenoid but there was no 240v. Fault finding chart says replace PCB but i did that qalready!!!!
acording to manual the normal lighting sequence is so
1- the fan runs - check
2- the air pressure switch operates - check
3- the first pilot solenoid valve opens -
4- the sprak igniter operates
5- pilot lights
6- ignition spark switches off
7- second solenoid opens giving main burner operation
from what i read the gas solenoid must work in order for spark to commence but board is not sending 240 to solenoid...
this has left me confused so any help guys is really appreacited
cheers
DD368
Last edited: