called glow worm to a flexicom 30 as its still under warranty - been running fine for about 1.5 years - customer had power cut then had problems with boiler faulting with F1 . gloworm engineer replaced gas valve and worte on sheet gas valve changed and boiler serviced but isolated due to only 4mb wking pressure at boiler 20mb at meter.i went today as customer was worried it had been installed wrong- i got 19.5mb wk press at test nipple under boiler and 17.5mb on gas valve (manual says this boiler ok at press as low as 15mb).I then did a gas rate and the 30kw boiler was gas rating at 44kw gross way to high,no wonder the wk press was only 19mb under boiler .the boiler is fed in22mm pipe.my question is how could the engineer have serviced it if he was only getting 4mb wk press and what would cause this high gas rate.i was thinking the pcb could be faulty causing the fan to run to fast .i phoned glowworm who said the gas valves are standard and preset to suite any of the flexicom boilers and need no adjustment.anyone got any idea