A

alibryant69

hi i have just installed to 15kw grant ashps to a 16th century manor rebuild and a grant 26kw oil boiler to meet the demand for heat and water when the ashp's dont meet the demand, the whole systems set up correctly through a low loss header in the basement... but my problem is the air sources are drawing close to 300 amps when the start up, this spike happens at least 30 times a day and everyone else in the area has problems with their lights etc when this happens, the electric board are now threatening to cut the power to the house... when we went back to grant they didnt have a clued and kept fobbing us off with excuses like they have come out to look at it when they havent and they are making something to fix this??? which if they havent looked at the ashp's how can they know??? has anyone else out there had any similar problems?? many thanks alastair
 
Hi,

Is the back up immersion 3kw or (6kw available) kicking in?

That would explain the extra Amps

Edit just noticed the 30Amps includes 3kw immersion but they may have 6kw heaters but that wouldn't take it to 80 Amps?
 
Last edited by a moderator:
In Response...

When the current is high i.e going to 80Amps no the immersion heaters are not on the ones we have only have the 3kw heaters.
But in the paperwork it clearly states that the total load is 30Amps should these figures include when the heaters are on?
the label on the rear of the ASHP states that it's running current is only 11Amps but we were told those stickers are not for the U.K market which makes no sense at all as no matter where in the world it is the calculation for the amps on a 240V machine remains the same i.e
watts divided by volts gives you the amps
 
how long has the 80 amp current been happening? is it recent or has it been for quite a few months

This has been an ongoing problem since around October 2010 they haven't run correctly since they were installed....
they only go into the 80Amps when in De-frost mode. You can hear the compressor getting harder and harder to spin as if there is supposed to be a solonoid to switch over for its de-frost cycle but it doesn't open. so the pressure builds and builds therefore causing the current to creep up and up as the pressure builds. sounds like its just gonna blow up when it reaches its peak the whole ASHP is going to shake itself to bits...
 
You need a refrigeration engineer to evaluate the refrigeration/electrical circuits, Where are you based ?

I agree but while Grant have not yet started their warranty it has to be up to them to repair it if we get an independant engineer to look at it or possibly sort it out will this not then result in them cancelling any warranty?

I'm sure if I delved in deep enough I could probably sort it but it's not my responsibillity I just feel sorry for my customer that has them fitted...

also info not stated yet is that when the units were first put in they come fitted with an outside air temp sensor... when the units froze up in the very cold winter we had the first thing they did was to disconnect the air temp sensor and fit a resistor in its place so now they are still going into a de-frost mode but surely in this milder weather they should never need to go into this de-frost mode where they essentially just waste heat blowing it outside... which in turn makes them uneconomical when this is mentioned to Grant they tell us that all the units are now being done like this... going back to them telling us we have the only units that are playing up why would they roll out a second rate modification that forces the units to use more electricity.
 
Like I said they are only going into De-frost mode due to the fact they have disconnected the outside air temp sensor and replaced it wit a resistor which is ther to fool the controls into thinking it is colder than it is
 
If I were in your position or the customers I would be would getting Grant out everyday until they got the unit working correctly. If Grant claim that the units are working correctly then clearly the unit is not fit for purpose and should be removed and the customer gets their money back and some compensation
 
Most definatley Grant responsability I have on many occasions evaluated underperforming systems as an independant 3rd party and have never yet failed to get a positive result from the manufacturer
 
If I were in your position or the customers I would be would getting Grant out everyday until they got the unit working correctly. If Grant claim that the units are working correctly then clearly the unit is not fit for purpose and should be removed and the customer gets their money back and some compensation

My thoughts Exactly...
 
Most definatley Grant responsability I have on many occasions evaluated underperforming systems as an independant 3rd party and have never yet failed to get a positive result from the manufacturer

Are you talking about probs with ASHP's if so have you had any dealings with Grant?
 
I agree with Unguided1, get grant out asap and the weather comp being by-passed is a joke

like I said in earlier posts Grant do come to look at it but they can't wait to get back in the van and on the way back home due to the distance they have to travel and when contacted they seem very lax in coming to see them it can take weeks to get them there and when they leave they say they will put together a report on there findings but when we call them back eveyone denies any knowledge of previous visits
 
like I said in earlier posts Grant do come to look at it but they can't wait to get back in the van and on the way back home due to the distance they have to travel and when contacted they seem very lax in coming to see them it can take weeks to get them there and when they leave they say they will put together a report on there findings but when we call them back eveyone denies any knowledge of previous visits

I reckon that if you block their van in they have got stay as long as you do, and If it were my customer I would make sure that I turned up with a sleeping bag, mind you the giant thumb of doom hates it when I refer to her as my sleeping bag!!!!!!!!!!
 
Last edited:
  • Like
Reactions: 2 people
As Unguided says, block their van in or take a photo of them whilst they are looking at the unit. That way they cannot deny any knowledge of the unit/visit.
 