Yes I've worked it out thanks Shaun. Still getting used to my new phone 🤦‍♂️
That's it, it was in lotus 123 originally before excel was even heard of!!
I have just added another "box" to give a taste of a fairly typical (fully sealed) installation, its quite handy.
Thanks John mate. Question. Theres no mention of static head or system volume in these boxes. Why is that?
Re Static Head, I didn't include this is because I don't know where the EV will be located, if its located just above the boiler on the ground floor then you would add ~ 0.1 bar to the final pressure to get the maximum (and ) boiler system pressure, more significantly, but a bit unusual, if the EV was located in the attic then you would add ~ 0.4/0.5 bar to the final (EV) pressure to arrive at the maximum (and ) boiler system pressure, if in the hot press then add - 0.25 bar, and so on, with EV mounted above boiler (ground floor) then the pre pressure should not be less than 0.4/0.5 bar to ensure that you will get circulation through the upstairs rads on boiler start up.
Re System Volume, again I didn't include it directly in the calcs BUT I give a table with the % expansion for water temps from 50C to 110C, so for example if you estimate that your system contents are 100 litres and that the flow/return temps are say 75C/60C, mean of 67.5C...from the table this equals ~ 2% expansion so total expansion is 100*2% or 2 litres which you insert in the yellow box adjacent to "expansion"
You can see the calculations in the excel S.Sheet if you highlight each cell.
Reactions: SJB060685
Thanks John. I was overlooking thermal expansion coefficient on the left of boxes 🤦‍♂️
[automerge]1578166817[/automerge]
How would an expansion vessel under charged at ground floor level affect circulation in upstairs rads on start up @John.g?
might be best to start a new thread as im sure theres more people who would like to learn this information
I'll just answer this and maybe some one can/would transfer these posts to a appropriate thread.
If, for any reason, the pre pressure and fill pressure (due to leakage or improper charging or whatever) fall below the static head then the water level will start falling in the upstairs rads (first) and because the circulating pump is just that, a circulating pump, eventually there will be no circulation upstairs, after start up , and depending on the water temperature, the EV pressure will start to rise and may provide enough pressure (head) to allow circulation through these rads again. IMO poor or failed upstairs rad circulation is a indication of EV/water leakage problems.
Or to put it another way, if you pre charged to say 0.3 bar and initial filled to 0.3 bar then IMO there will be no upstairs circulation.
One of our installers currently fitted a new heat only boiler to replace an old floor standing with gravity hot water. At the time he never fitted any valves or cylinder stat etc so I have been called back there to basically start again. Been there today to do it and found that he had the pump on the return. Anyway I drained system and made the necessary alterations to the pipework by the boiler and fitted a mid position valve and a wireless cylinder stat (as the run is impossible to get a cable between the two). So currently the feed from the F + E tank goes into the return of the cylinder and the vent on the flow. The boiler is in a tight cupboard low to the ground in an extension of the side of the house and the cylinder is on the 1st floor in the middle of the main part of the house so you can imagine how the pipework runs
Hi all just thought id update you with todays result. So i did what i thought was best and fitted and 18 ltr vessel above the boiler, took out the f + e tank and fitted AAV's on the feed and vent pipes from the cylinder coil. works an absolute treat.
Reactions: John.g
Yes I understand how low water pressure can result in no circulation of upstairs rads, especially when you say it's a circulator and not a lifter which some people misconceive. I had however overlooked low EV pressure and it possibility acting as an accumulator
Reactions: John.g
So now, a fully sealed system.