Grundfos pump making unusual sound/boiler not coming on
View the thread, titled "Grundfos pump making unusual sound/boiler not coming on" which is posted in Boiler Advice Forum on UK Plumbers Forums.
First post so greetings to all!
We have a problem with our elderly Potterton boiler and its Grundfos pump as follows:
  • Boiler started behaving erratically, switching on & off at short intervals
  • Within days boiler stopped coming on at all
  • Noticed that Grundfos pump was making an unusual sound as though struggling to function
  • Tried method shown here without success:
Am I correct in assuming that the boiler is not working due to loss of pressure because the pump is not circulating the water through the system?
  • NOTE that when the programmer was replaced a couple of years ago with a Drayton Lp112 the person installing it wired it incorrectly so that the heating and hot water could not be controlled separately. It has been like it ever since.
We would appreciate advice as to how to best tackle this problem, bearing in mind the following:
  • We are looking for a short term affordable solution as we will be moving house in the next 12-18 months
  • We do not have the funds for a full system replacement at this time
Many thanks!
Stephen
Greetings Stephen, I’m confused, has the boiler lost pressure and now not functioning, or is it the pump noise or both? Which potterton boiler? are you bothered for now about fixing the programmer?
1. If the pump spindle is not turning when the pump is on, then it has a fault.
2. If water is not circulating fast enough, the boiler will overheat and turn itself off. Its not a pressure issue, more a flow one.
3. Not sure about your boiler, but some will detect whether pump is running or not, and if not will not turn on.
4. I suspect you are going to need a new pump. As you have a system boiler with the pump inside you are probably forced to buy one at Vaillant prices and pay to have it fitted by a Gas Safe registered person.
5. There is a possibility that a circuit board fault, or other boiler internal fault, is causing the pump not to start, but given that it was making unusual noises, this seems unlikely.
6. I think your first port of call should be a boiler repair person, preferably one with Vaillant experience. Some manufacturers do a "fixed price" fault repair service. Worth finding out if Vaillant do this if you can't find someone locally.
Hi there
Many thanks for the fast response! And thanks in advance for any advice you may be able to give me.
I'm confused too, which was the reason I posted my query here. The extent of my understanding of the problem(s) was listed in the bullet points of my first post.
The boiler is a Potterton Netaheat Profile of indeterminate age. It has no external pressure gauge so (as a lay person) I have no way of telling whether it has lost pressure. My question was as to whether the pump (Grindfos Selectric UPS 15-50) malfunctioning would cause loss of pressure that would prevent the boiler from coming on at all. Or to put it another way, whether I have one problem here or two separate problems that have coincided. Note that the pump body gets hot when the system is switched on but the pipework around it does not.
Its not essential to have the programmer correctly rewired at the present time, but if the overall solution to the immediate problem was the replacement of the pump only, it would be preferable if it could be done at the same time.
Many thanks again!
Ok, so you have tanks in the loft then - not a pressure gauge. So a lack of water in the system, a sticking pump or faulty capacitor (but like a starter motor) could cause this issue. I suspect the pump isn’t circulating as you have kind of describe, so follow the video you posted and try and turn the pump/circulator shaft. If the pump sounds like it’s trying to kick in, but just a slight humming noise, then i suspect the capacitor. If the heating system worked recently, but has stopped I suspect the water in the system is fine.
Thanks for your helpful reply. Just to clarify the boiler is a Potterton Netaheat Profile and the Grundfos Selectric UPS 15-50 pump is in the airing cupboard.
OP has Potterton boiler, the video is just a link to YouTube, using a Vaillant pump, obviously causing the confusion.
Ah that's great as you seem to have eliminated two out of three of those possibilities. I did try the method shown in the video and the pump impeller was turning freely. I have also checked the small tank in the loft and it is full. Which seems to leave just the capacitor. I should mention that the fault actually occurred a few weeks ago but we have been managing for hot water with the electric immersion heater. Would you anticipate having left the system idle for this length of time causing any additional problems? Many thanks again.
No I wouldn’t. When you spun the impeller, was there a demand on, eg heating or hot water?
Thanks again for all your replies. Apologies if I am misunderstanding your question but the boiler and programmer were both off when I spun the impeller with a screwdriver. I thought this was correct.
If it springs into life when you try it with power on, then new capacitor or pump required.
Just tried that. When I removed the centre screw the impeller screw head was visibly turning but the pump was still making the same abnormal sound and the boiler is not igniting. The same sound can be heard in the boiler cupboard. Difficult to describe but it sounds as though water is trying to circulate around the system but certainly not running smoothly. The pump is old, would it be practical or indeed sensible to replace the capacitor only, or would it be wiser to replace the entire pump assembly with a new one? Many thanks
Time to move on and change pump
Dab evosta 3 is our replacement pump of choice.
Better price than grundfos and Dab is owned by grundfos!
Can’t it’s inbuilt to the boiler and has to be original
It’s a YouTube link showing a repair (general video), hence why steadyon mentioned Vaillant, boiler is potterton.
Video shows the pump in the boiler
Apologies for the confusion I have unintentionally caused by posting the link to this YouTube video. I linked to this as a reference to something I had already tried to free the impeller. I hadn't realised that the link and video 'thumbnail' would appear as a huge image within the post!
Belated thanks for all your help with this. Work has now been done. New Grundfos UPS3 15-50/65 pump fitted and controller now correctly wired so water and heating can be programmed independently. He also changed the 3-port valve as it transpired that the person that wired the replacement controller incorrectly also fitted the wrong type of valve for the system. Boiler and system is now running the most efficiently it has for years. However there is now a noticeable hum resonating through the system that builds up shortly after it switches on. Strangely it seems louder in the downstairs cloakroom than it does in the airing cupboard itself. If you hold the pipes adjacent to the pump there is a slight vibration that seems to correspond with the frequency of the hum. Any helpful suggestions gratefully received. Thanks!
The UPS 3 is a very powerful pump and if set very high can cause problems, can you take a photo of the settings, they will correspond to one of these settings.
It comes factory set to its max, constant curve iii
Thanks John
It does seem to be set to the factory default. I have attached a couple of photos, one of the non-working original pump and one of the new UPS 3. The orientation of the UPS 3 is as seen (i.e. the photo is the correct way up).
As I said previously the system is running really well apart from the resonating noise. What setting would you suggest? The boiler is an old Potterton Netaheat Profile (annually serviced).
Many thanks again
Hi Stephen,
Would suggest either PPII, which is nominally 3.8M but should run at around 2.5/2.6M at your demand OR CPI which runs at a constant 3M head.
CCIII meant you were more than likely running at a 6M head, no need, this is only used on pump installation and should be only run at this head for about 10 mins to assist in venting air.
You probably know how its done but press and hold the setting button for 3 secs to change pump modes, then briefly press to select the correct mode setting.
Hi Stephen,
Thanks John. We tried that. In PPI, PPII, CPI & CPII setting the LEDs remained flashing and the pump didn't start running. We put it back into Constant Curve mode and selected CCII mode. It seemed to be struggling on CCI. Are we missing something obvious here? Many thanks again for your time and helpful advice John.
ALL the PP & CP modes operate with flashing LEDs (see below) so if lighting in any of the modes below as shown then the pump will/should be running. (but very quietly)
What do you mean by struggling?.
If CCI is too weak at 4.2M then not a hope of enough circulation on PPII or CPI.
If happy with CCII at 5.2M then leave it or perhaps try CPII at 4.5M which may give quiet running with enough head.
Thanks John. Ah OK didn't realise that the LEDs were supposed to flash. When I said struggling I just meant that the pump didn't start straight away, not sure what would have happened if I had given it time? On CCII one of the radiators didn't heat at all and another was lukewarm. Now the boiler has switched off and all the radiators are cooling down. No resonating noise at CCII but it's looking like the system only supplies all the radiators at CCIII which is somewhat concerning bearing in mind your previous remarks. Note that our system ran well for many years with our old Grundfos Selectric 15-50 pump until it failed recently. Would the type of 3-port valve fitted have any bearing on this? It's a Drayton. Apologies for my lack of knowledge regarding this stuff and thanks again for your advice. Stephen
What is the boiler power and is it a modulating boiler?
How many rads?.
IF the UPS3 is working properly then CCII is more powerful than CC3 was on your old 5M selectric.
The UPS3 on CCII will maintain +5M up to a demand of 1.1 m3/hr, 18.3LPM.
Also, there should be little or no delay in pump startup after changing settings.
Is the system clean as very dirty systems can build up magnetite on these pump rotors which can slow them down or stop them, the pump head can be removed for cleaning.
What was the old pump like eg in the outlets of the pump any blockage or was it clean and around 15mm dia ?
Here is the Selectric 15-50 Pump curve which gives a head of 4.2M @ 1.1m3/hr (0.306 l/s) on CC3 vs the UPS3's 5M @ 1.1m3/hr 0n CC2 so something amiss.
How many rads?.
Hi John. Thanks for all the information you have provided. This is a steep learning curve for me as I am a complete layman and unfamiliar with the terminology and power ratings etc. But this is what I do know:
Boiler is Potterton Netaheat 50e which Google tells me is max. 14.65kw output
We have 10 radiators in all, smallest 72cm, largest 180cm
4 radiators + heated towel rail upstairs
3 long + 2 short radiators downstairs
The engineer drained, refilled and added inhibitor and fitted new valves with the new pump and 3-port valve.
When we put the pump back into CCIII after everything switched off on CCII last night the pump was ‘throbbing’ and making a ‘thrum-thrum-thrum’ sound as it was running. We left it for a few minutes to see if it would return to normal. It didn’t so we turned it off. This morning there was a lot of gurgling and ‘ticking’ but it is now running on CCIII as before. All radiators are hot. The resonating noise is back.
Many thanks again.
Stephen
Looks definitely like a pump problem there IMO, there were a few "dud" UPS3s sold, I would inform your engineer as a new pump should be supplied without question, under warranty, except that your system was/is filthy.
You can yourself just ensure that the pump isol valves are fully open and just recheck that the pump is orientated correctly, ie, if on the boiler flow side, pumping away from the boiler and if on the boiler return, pumping into it.
Thanks John. Sadly I don't know how to check these things. The pump itself is physically mounted upside down, presumably as if it were the 'correct' way up the mains cable and its mounting would prevent the airing cupboard door from closing. I have attached a few photos. A couple of further things to mention that may or may not be relevant.
1. Our system has no wall-mounted thermostat. We have old Servowarm thermostatic radiator valves on each rad.
2. We usually run the boiler on setting 3-4 on the control dial (range 1-5/max).
Thanks again!
There is an arrow on the pump body, see if its pointing up or down, then follow the pipe (up or down) and see where its attached to the diverter valve and we can soon figure it out.
The pump valves, just turn each one clockwise until shut then anticlockwise until fully open, it should take ~ 3 to 5 full turns each way to fully close/open them.
Didn't notice attachments before.......if the arrow on the pump body is pointing downwards then the pump is installed correctly.
Reply to the thread, titled "Grundfos pump making unusual sound/boiler not coming on" which is posted in Boiler Advice Forum on Plumbers Forums.
Stephen JW,
Stephen JW,