Yes, that's basically it, have a read of this.
Constant flow automatic bypass valves | Page 3 | PlumbersForums.net

Re your query on condensing effect, it can/will have a effect but this is dependent on the boiler return temp as condensing doesn't begin until ~ 55C. Using a few numbers, if your boiler requires 4 LPM minimum flow and assuming a boiler temp of 70C with a return of 50C and a flow rate of 10 LPM with no by pass, because of the constant by pass you will have 10 LPM at 50C mixing with 4 LPM at 70C resulting in boiler return of 55.7C so a loss in condensing effect, if the flow through the rads was only say 4 LPM (if TRVs fitted) then the return may only be 45C but mixed with the 4 LPM bypass at 70C will result in a boiler return of 57.5C, not hugely different in temperature but a fairly significant difference in condensing effect.
Condensing Temperatures.png
You can see the effect of the different return temperatures here on boiler efficiency.
 
Excuse me for jumping in on this thread but just fitted a Grundfoss UPS3 pump time my central heating and in PP 1 or 2 when running the less continually flash, is this correct!
 
As below, the yellow or yellows flash, I think, depending on which mode is selected. Would suggest PP2 as PP1 is very weak at 1M to 2M, PP2 gives 1.9M to 3.8M.
1632571109342.png
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Grundfos UPS3 Pump Modes" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
IanGMT,
Last reply from
John.g,
Replies
37
Views
31,205
Back
Top