Matt0029

Gas Engineer
If changing a combi boiler system to a heat pump. What do they usually do with the balanced cold connection on the hot water cylinder? Cap it. And put a pressure reducer on the mains so they have equal hot and cold pressures? I can't see them repiping a balanced cold from the cylinder to each cold feed appliance that is of a mixer valve type. Thank you.
 
If its a combi its likely you'll have 15mm colds and hots everywhere so I would probably be looking at re-piping to 22mm plus putting in the balanced cold to allow the outside tap and kitchen sink to remain at street pressure. If its just a single bathroom then possibly do as you've suggested, but future proofing it is a good selling point to the customer and more money in your pocket.
 
Sorry yes I didn't think about that. Unvented cylinders usually need require a 22mm supply. Could be a re pipe from stop tap? But some are installing this systems in a day in a team of 3 or 4.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Heat pump unvented install balanced cold" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

Matt0029

Gas Engineer
Joined
Location
leeds
Member Type
Heating Engineer (Has GSR)

Thread Information

Title
Heat pump unvented install balanced cold
Prefix
N/A
Forum
UK Plumbers Forums
Start date
Last reply date
Replies
10
Unsolved
--

Thread statistics

Created
Matt0029,
Last reply from
ShaunCorbs,
Replies
10
Views
1,464

Weekly or Monthly Email Digest

Back
Top