Is anyone able to give me some advice on a potential problem with a Worcester combi we looked at today please.
Customer reported hot water on bath only getting luke warm. On first inspection we found the diverter valve passing heat down the central heating flow, so we've cleaned all the crap off the paddle on the diverter and given the plate hex a clean (which was pretty clean anyway). Diverter valve now working as it should but still only luke warm at the bath taps.
When reducing the flow down to 6l/m it starts to get hotter but MI's state it should be giving a temp rise of 40C at 10l/m, which it isn't getting anywhere near.
DHW temp sensor has been tested and giving correct readings. Boiler sounds as though its fired at full rate when the taps running. Flue gases were adjusted to MI's recommendations and gas rate fine.
We tried to get a temp reading of the primary hot pipe coming from the top of the heat exchanger and looks to be reaching 50C maximum. Surely this should be a lot hotter if its then got to heat DHW in the plate. Maybe the primary flow NTC sensor???? Anyone had anything similar of offer advice?
Much appreciated
Ash
Is anyone able to give me some advice on a potential problem with a Worcester combi we looked at today please.
Customer reported hot water on bath only getting luke warm. On first inspection we found the diverter valve passing heat down the central heating flow, so we've cleaned all the crap off the paddle on the diverter and given the plate hex a clean (which was pretty clean anyway). Diverter valve now working as it should but still only luke warm at the bath taps.
When reducing the flow down to 6l/m it starts to get hotter but MI's state it should be giving a temp rise of 40C at 10l/m, which it isn't getting anywhere near.
DHW temp sensor has been tested and giving correct readings. Boiler sounds as though its fired at full rate when the taps running. Flue gases were adjusted to MI's recommendations and gas rate fine.
We tried to get a temp reading of the primary hot pipe coming from the top of the heat exchanger and looks to be reaching 50C maximum. Surely this should be a lot hotter if its then got to heat DHW in the plate. Maybe the primary flow NTC sensor???? Anyone had anything similar of offer advice?