Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

How many rads from a 22mm pipe?

View the thread, titled "How many rads from a 22mm pipe?" which is posted in UK Plumbers Forums on UK Plumbers Forums.

S

srobbo180

I am planning to add a radiator in a shower room. I am able to access the 22mm flow and return pipes that run through the room. The pipes end in manifolds that currently feed 4 radiators. Am i ok to tap into the 22mm pipe before the manifolds to feed 1 rad or will this have an adverse effect on the remaining 4 rads.

Thanks

Simon
 
It depends on several factors. Does your boiler have enough power to heat the new radiator? How big are the other radiators? A 22mm pipe will feed a lot of radiators as long as the boiler is up to it. You may well find you have to rebalance the remaining radiators after you install the new one though.
 
Pinched this from another site ... I knew there was some data somewhere regarding what heat a pipe could carry!!! So it's not how many rads but how much heat is needed... I have no idea whether the info is true but it sound good 🙂 here you go:-



"The heat carrying capacity of a tube is limited by the maximum velocity that can be accepted for noise reasons. This is generally taken as 1.5 m/s. The other key factor is the temperature drop of the system which is generally taken as 20°C for a condensing boiler, although greater or lesser temperature drops could be specified.

For 1.5 m/s and 20°C temp drop, the carrying capacity of each pipe size is as follows -

8mm = 4.5 kW, 10mm = 7.3 kW, 15mm = 18.1 kW, 22mm = 40.2 kW and 28mm = 67.5 kW. "
 
Pinched this from another site ... I knew there was some data somewhere regarding what heat a pipe could carry!!! So it's not how many rads but how much heat is needed... I have no idea whether the info is true but it sound good 🙂 here you go:-



"The heat carrying capacity of a tube is limited by the maximum velocity that can be accepted for noise reasons. This is generally taken as 1.5 m/s. The other key factor is the temperature drop of the system which is generally taken as 20°C for a condensing boiler, although greater or lesser temperature drops could be specified.

For 1.5 m/s and 20°C temp drop, the carrying capacity of each pipe size is as follows -

8mm = 4.5 kW, 10mm = 7.3 kW, 15mm = 18.1 kW, 22mm = 40.2 kW and 28mm = 67.5 kW. "

Interesting that, they seem a bit on the heavy side, this is old money, I was always taught 15mm carried just over 13,000 btus. But its a long (long, long 🙂 ) time since I did all that.
 
Looking at my last post I thoughtthey were a bit excessive so I did a bit more delving ... The table below looks a bit more realistic! I've put a link to the web page also ... Blinkin DIY not.com!!!

Nominal Pipe size Internal Area (m2) Water flow rate (litres/sec)Maximum theoretical heat flow rate. (Ignoring resistance)
(Kwatts )

8mm - 2.5kW
10mm - 4.2kW
15mm - 10.3kW
22mm - 23.4kW
28mm - 39kW

That looks a bit more realistic 🙂

Central heating pipe sizing
 
Last edited by a moderator:
It will be fine, just connect it up, you might have to rebalance a few rads but I doubt it.
 
Pinched this from another site ... I knew there was some data somewhere regarding what heat a pipe could carry!!! So it's not how many rads but how much heat is needed... I have no idea whether the info is true but it sound good 🙂 here you go:-



"The heat carrying capacity of a tube is limited by the maximum velocity that can be accepted for noise reasons. This is generally taken as 1.5 m/s. The other key factor is the temperature drop of the system which is generally taken as 20°C for a condensing boiler, although greater or lesser temperature drops could be specified.

For 1.5 m/s and 20°C temp drop, the carrying capacity of each pipe size is as follows -

8mm = 4.5 kW, 10mm = 7.3 kW, 15mm = 18.1 kW, 22mm = 40.2 kW and 28mm = 67.5 kW. "

The total wattage for the rads I have on that pipe is 6178 if i am correct that is 6.178 KW so that gives me plenty to play with?
 
Interesting that, they seem a bit on the heavy side, this is old money, I was always taught 15mm carried just over 13,000 btus. But its a long (long, long 🙂 ) time since I did all that.

They did to me too SimonG hence the bit more research... Dodgy plumbing websites full of nonsense!! lol
 
last year i fitted 3 P+ rads on 15mm ,in total there was 18 i think ! I thought customer is going to work but just about !
he was happy to go for it so I did it ! re balanced the system and it worked but it needs one more exp vessel !
I think this winter will be new boiler for him ! as old one it was only 28cdi the old wb !
 
I am planning to add a radiator in a shower room. I am able to access the 22mm flow and return pipes that run through the room. The pipes end in manifolds that currently feed 4 radiators. Am i ok to tap into the 22mm pipe before the manifolds to feed 1 rad or will this have an adverse effect on the remaining 4 rads.

Thanks

Simon

you should not have any issues,but what system do you have combi or conventional?
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "How many rads from a 22mm pipe?" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
srobbo180,
Last reply from
Billy Bob Bob,
Replies
13
Views
20,245
Back
Top