P
Plumb Ugly
Got the above boiler with L9 fault appearing seemingly randomly, its happened about half a dozen times since just before xmas. The manual says its an overheat on the heat exchanger and to check the system is full, vented and that the pump is running correctly and to check the thermistors. Iv done all of the above and checked the circulation with temp clamps on the flow and return with both ch and hw on, just the ch, just the hw, ch with all trv's shut and with both zone valves closed and circulating through auto bypass. The temp differential has never exceeded 15C in any of these senarios and the fault has never occured while i have been there annoyingly. The system pressure is just above 1 bar cold and rises to just under 2 when hot, the auto air vent on the boiler is working. The house is 5 years old and the water i drained off was crystal clear. Has anyone else experienced this fault?