This is the only way of determining whether the boiler is working as per the spec. The cold incoming water temp in the winter makes the hot water cooler. Check the manual for what temperature rise you should be getting at what flow rate, so like 11 l/min at 35 degree temp rise. The incoming main will be about 10 degrees roughly at this time of year so with a flow of 11l/min you should see a water temp of 45 degrees as an example.
I just had another look at the manual.
It says dhw flow rate is 12.4. If the flow rate is over this, it will affect the operation in hw mode?
Is this what you mean?