Couple of quick questions. How do you set this boiler to go into CO mode ? Also can you take a burner pressure on the boiler or is it just easier to do a gas rate at the meter
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
QC guy was on a job with me and said if boiler has been installed within last year then gas rate and fga is satisfactoryYour not doing a service then are you? U need an 8 mm ring spanner and a mug ( to pour water through) flat head ph2 and shifter. If you don't wash out hex the boiler will be goosed in 2 years as primary bakes and splits , or trap blocks. Do it to the mi or just get your self a sticker for van "fga cowboy" I can strip rebuild logic and inlet pressure in 10 mins max . Isar almost same .
You get inlet pressure on gas tap. Each input range has a different standing loss across tap so check mi. Also you can get current values by turning DHW and ch to min and holding reset for 10. You get list of most recent faults first.
Be interesting that the company you work for have actually told you not to follow mi? U got it in paper?
QC guy was on a job with me and said if boiler has been installed within last year then gas rate and fga is satisfactory
I'm going to start doing this. Cheers for the infoOk.
Power off
Undo 15mm nut on fan
Pull leads off fan
Undo securing stud on fan
Lift fan out.
Undo two ph2 screws on flap on silencer, lift silencer up and then out at bottom. It's a tight fit. Put two screws and flap back on TIGHT!
Undo two front and two rear 8mm nuts. Lift hex lid on to side, slide out lhs of boiler.
Rinse 3 pints of water through hex
Clean sump.
Check electrodes and burner head and gasket.
Re assemble
Gas rate and inlet.
surely ordering a gasket set in advance would be wise do you have a part number you can add so the guys reading this go armed with oneOk.
Power off
Undo 15mm nut on fan
Pull leads off fan
Undo securing stud on fan
Lift fan out.
Undo two ph2 screws on flap on silencer, lift silencer up and then out at bottom. It's a tight fit. Put two screws and flap back on TIGHT!
Undo two front and two rear 8mm nuts. Lift hex lid on to side, slide out lhs of boiler.
Rinse 3 pints of water through hex
Clean sump.
Check electrodes and burner head and gasket.
Re assemble
Gas rate and inlet.
Cheers for all the tips. This site has proved invaluable to me and that's only been 2 months out on my own 🙂