Went to service logic heat 15 today with complaint of L2 showing and having to reset to get it going . Hadn't been serviced in five years from new ... The heat exchanger and siphon were gunged up with aluminium oxide sediment , cleaned thoroughly., cleaned spark and sensor probes ,checked flow and return thermistors, checked gas jet and Venturi feed to fan , Flue is clean .Gas pressure 19mb operating . Rang Ideal in desperation but the guy I spoke to couldn't suggest anything I hadn't already checked . Anyone any ideas ? Thanks in advance .
Sorry , boiler runs for about ten minutes well behaved ,FGA spot on ratio .0006. It then either gets up to heat and restarts or makes a few attempts to and then locks out with L2 displayed . System is filled with water , pump running fine , rads heating .
Sorry , boiler runs for about ten minutes well behaved ,FGA spot on ratio .0006. It then either gets up to heat and restarts or makes a few attempts to and then locks out with L2 displayed . System is filled with water , pump running fine , rads heating .