N
neily01
Could I get abit of help off of you kind people reguarding an ideal mini. Went to a boiler with a descent leak out of the diverter valve section, so much I could see the water bubbling out of the elec connections on the actuator. Replaced the whole flow section and actuator and after refilling the boiler worked fine in ch mode but would now engage the pump flow switch in hw mode. After a bit of running and clearing of air the hw worked ok now after the weekend have had a call to say no hw without heating on so I am guessing the same fault. The main hex is well on the way to being blocked so guessing the same with the plate, could both the hexs being blocked restrict the flow enough to stop the pump flow switch fully coming out? On a side note the pump seems strong and it is the only thing on the boiler that seems to work well, did suggest to the cust that a new boiler would be the way since the diverter plus act was nearly £300 and the rest of it was knacked. Any help would be great.