Hi all, I'm just after some knowledge to something i came across today. I was asked how a direct unvented cylinder worked in an apartment a few doors down to where i was working. The couple just moved in and wanted some advice, They had only been in the apartment for two days and used to have a combi system. The cylinder wasn't heating up over night and they had to constantly use the boost and the controls were not working at all.
I made safe the electric and opened up the control box and saw what is in the picture attached to this thread. One wire from one RCD feeding both immersions, the controls completely by passed. I was just wondering why they had done this as i am interested. Also wanted to know if one 20amp breaker is suitable for two immersions around 3kw's each.
I have asked them to get an electrician in. Then i can sort out the cylinder as the expansion vessel is flat and the check valve is before the tee off to the cold feed to bathroom and kitchen and D1 for the expansion relief runs uphill 600mm, been there since 2001 with no paperwork.
Cheers.
I made safe the electric and opened up the control box and saw what is in the picture attached to this thread. One wire from one RCD feeding both immersions, the controls completely by passed. I was just wondering why they had done this as i am interested. Also wanted to know if one 20amp breaker is suitable for two immersions around 3kw's each.