Hi,

I noticed yesterday that when my HW is on, that the boiler runs constantly... I even tested this morning after it ran last night so no water usage overnight and it ran for 30 minutes before I turned it off on the controls. No dripping from Tundish.

My suspicion is the thermostat in the Megaflo which presumably is demanding heat continually. The boiler temp is 60c so it isn't going to overboil the water the cylinder as it reaches an equilibrium.

I'm not G3 qualified so cannot do any real troubleshooting myself but the three way zone valve appears to be operating correctly and hot pipe out of this is then fed into the two way zone valve. There is no resistance on the lever on the two way valve which indicates to me that it has power, presumably by virtue of the HW being on on the controls and the cylinder stat calling for heat.

I'll ask my plumber to take a look but my suspicion is the cylinder stat at this stage unless there is a flaw in my logic. Could a faulty 2 way zone valve cause it to remain in the open position and demanding HW heat continually? I think not as otherwise it would continue running when the HW was turned off on the controls.

Thanks...
 
If the boiler stat and the cylinder stat are both set the same, or if the boiler stat is set lower than the cylinder stat then the cylinder stat will never be satisfied and the boiler will continue to run, the boiler stat should be set at least 5C above the cylinder stat set opoint.
 
If the boiler stat and the cylinder stat are both set the same, or if the boiler stat is set lower than the cylinder stat then the cylinder stat will never be satisfied and the boiler will continue to run, the boiler stat should be set at least 5C above the cylinder stat set opoint.
Thank you, and I understand this, but nothing has changed. This appears to have just started happening.
 
Thank you, and I understand this, but nothing has changed. This appears to have just started happening.
Just increase the boiler set point temperature (even temporarily) to 70C, see if the boiler then stops eventually on HW only.
 
If the cylinder stat is satisfied the valve will close, stiff resistance when pulling on the manual lever, if the boiler then keeps running then its the end switch in the valve but I think you said the lever is loose which means the valve is still powered open. Maybe just switch off all power and check the valve is closed, stiff lever resistance.
Then restore the power but just programme off the HW, valve should remain closed.
 
Last edited:
Wouldn’t say it’s that as it’s sensing the temperature they just normally fail

The temp probe is fully in the dry pocket ?
Well, i've eliminated the control valve or leak. If the stat fails, it may not tell the boiler shut off. I will adjust the stat down on the cylinder tomorrow but like I said, this hasn't been touched. I have my plumber coming to do some other work so will have him take a look and troubleshoot correctly.
 
Well, i've eliminated the control valve or leak. If the stat fails, it may not tell the boiler shut off. I will adjust the stat down on the cylinder tomorrow but like I said, this hasn't been touched. I have my plumber coming to do some other work so will have him take a look and troubleshoot correctly.

Boiler temp been knocked down ?
 
Valiant EcoTech 637. It's a Y system, with a 3 port valve into a 2 port then into the UVC.
The default position of a MPV is HW which should sent 230V to open the 2 port valve with HW programmed on and a call from the cylinder stat, the 2 port valve end switch then sends 230V to fire the boiler, the two port valve should close when the cylinder stat is satisfied or when the HW is programmed off, I think you said it does close and the boiler shuts down when the HW is programmed off so looks like the cylinder stat. If it doesn't close when the HW is programmed off then it might be getting 230V from the MPV orange wire.
 
Just a reminder that thermostats on unvented cylinders, such as Megaflos, must be serviced and repaired by someone who holds a current unvented hot-water systems ('G3') qualification.
 
Just a reminder that thermostats on unvented cylinders, such as Megaflos, must be serviced and repaired by someone who holds a current unvented hot-water systems ('G3') qualification.
Although the process of swapping it is straightforward, I will have my plumber who is suitably qualified firstly confirm my fault determination and then swap the stat.
 
Well, i've eliminated the control valve or leak. If the stat fails, it may not tell the boiler shut off. I will adjust the stat down on the cylinder tomorrow but like I said, this hasn't been touched. I have my plumber coming to do some other work so will have him take a look and troubleshoot correctly.
Have you adjusted the stat??, with the boiler firing keep turning the stat down until the boiler stops firing, then turn it up slowly until the boiler refires, there should be ~ 6C to 10C difference (hysteresis) and you should also hear the stat clicking, if the stat has a index, note the two settings.
 
Have you adjusted the stat??, with the boiler firing keep turning the stat down until the boiler stops firing, then turn it up slowly until the boiler refires, there should be ~ 6C to 10C difference (hysteresis) and you should also hear the stat clicking, if the stat has a index, note the two settings.
Not on the Megaflo. I might give that go, I'm assuming this doesn't break any rules as I'm not G3 qualified but I see a thermostat as a user control.
 
@John.g @ShaunCorbs

So some more trouble shooting done this morning... I opened the cover on the thermostats for the Megaflo and the attached picture is what I have, indirect stat set at just over position 3 (this seems low). I reduced the temperature and after turning anticlockwise, I heard the 2 port diverter valve deactivate and the boiler ran for a few minutes on overrun until is shutoff. I then turned this setting back up to 3. The boiler fired back up but the cylinder stat did not shut off. After a while I increased boiler flow temp to 70 and then after a few minutes, once again I heard to 2 port diverter deactivate and the boiler shut down.

A few observations / thoughts here...

3 on the cylinder indirect stat seems very low but it is the same on the immersion. The water from the taps is very hot, you couldn't leave you hand under it for more than a few seconds, so it must be in excess of 60c. I know when using the immersion in the past that the water was also very hot. However, the recommendation for 60-65 from Megaflo is between 4 and 5.

I notice that although my Vailant boiler flow temp is set to 70, when the boiler stops heating the water but continues pumping, it lets the temperature drop to 54 before firing up again to bring the water back up to 70. Is this level of hysteresis typical?

Finally, unrelated to this problem, I noticed that an elbow on the copper pipe below the automatic air vent has a load of green verdigris on it. The rest of the pipe is free from this and it is insulated in foam. I took it off to feel the temp on the pipe back to the boiler. Is this anything to be concerned about? I can have my plumber take a look when I have him check the stat.

I hope that by doing what I've done today, I haven't broken any rules... After unscrewing the cover, it would be very easy to just swap this stat out myself but I believe that technically that would put in violation.
 

Attachments

  • IMG_3870.jpg
    IMG_3870.jpg
    729.6 KB · Views: 53
  • IMG_3876.jpg
    IMG_3876.jpg
    935.9 KB · Views: 46
Last edited:
@John.g @ShaunCorbs

So some more trouble shooting done this morning... I opened the cover on the thermostats for the Megaflo and the attached picture is what I have, indirect stat set at just over position 3 (this seems low). I reduced the temperature and after turning anticlockwise, I heard the 2 port diverter valve deactivate and the boiler ran for a few minutes on overrun until is shutoff. I then turned this setting back up to 3. The boiler fired back up but the cylinder stat did not shut off. After a while I increased boiler flow temp to 70 and then after a few minutes, once again I heard to 2 port diverter deactivate and the boiler shut down.
A few observations / thoughts here...

3 on the cylinder indirect stat seems very low but it is the same on the immersion. The water from the taps is very hot, you couldn't leave you hand under it for more than a few seconds, so it must be in excess of 60c. I know when using the immersion in the past that the water was also very hot. However, the recommendation for 60-65 from Megaflo is between 4 and 5.
Most stats are like the Cotherm. below, 10C to 70C, so 4.5 would seem to be correct for a setting of 60C, and 3=40C, its strange how your setting, if original was set to 3. I presume your stat has a hi limit trip incorporated in that stat, what make is it?.
I notice that although my Vailant boiler flow temp is set to 70, when the boiler stops heating the water but continues pumping, it lets the temperature drop to 54 before firing up again to bring the water back up to 70. Is this level of hysteresis typical?
Thats normal when the cylinder temperature gets close to the flow temperature, the boiler cycles on/off as the coil cannot absorb the minimum boiler output, the circ pump continues to run but the burner cuts out at the SP temp+5C, the burner will then not refire until the anticycle time has elapsed.

Finally, unrelated to this problem, I noticed that an elbow on the copper pipe below the automatic air vent has a load of green verdigris on it. The rest of the pipe is free from this and it is insulated in foam. I took it off to feel the temp on the pipe back to the boiler. Is this anything to be concerned about? I can have my plumber take a look when I have him check the stat.
Yea, get that checked out.
I hope that by doing what I've done today, I haven't broken any rules... After unscrewing the cover, it would be very easy to just swap this stat out myself but I believe that technically that would put in violation.
Can't advice on swapping out but it is advisable IMO to renew it even though you can reduce the setting to give say 60C cylinder temperature.

1721988608082.jpeg
 
Thank you.

My cylinder has two stats. The larger one at the bottom is for the immersion, set at 3 and the top one is the one for the indirect feed (boiler) which was set somewhere between 3 and 4.

Following this test, I put the indirect stat back at what it was and let the boiler run. It run for another 25 minutes at 70c and then the stat was satisfied. Water from the taps is hotter. Personally I think it's too hot. Anyway, I've ordered a thermometer off Amazon so I can check it and rule out any subjectivity.

I am tempted to swap out the stat anyway, they are inexpensive and it's operation seems to be suspect. What flow temperature should a system boiler ideally be set at? Is 70 the right setting anyway? We have 21 radiators on the system (not that they are in use now during summer). Boiler is in loft.

On the subject of the Verdigris on the pipe elbow. I'll ask the plumber to check it but there is no signs of leakage.
 
Is the one in the photo the indirect one and what is its make/model, what did you order??
Although it's not that clear, if you look to the top right of the photo, you will see another screw driven thermostat. Can't see the make. If you look to the top left you can see the thermal cut out stat.
 
One thing I wondered, is whether where the stat is housed, ifr they can get scaled up so they don't detect the temperature so easily... i.e. the stat sees a lower temp than is correct. I checked the temperature of the water from a tap and it's 54c.
 
One thing I wondered, is whether where the stat is housed, ifr they can get scaled up so they don't detect the temperature so easily... i.e. the stat sees a lower temp than is correct. I checked the temperature of the water from a tap and it's 54c.
Its a possibility but only if scale/limestone is building up in the bottom, the lower stat pocket which is for the immersion? should be even more scaled if this is true so maybe switch this in overnight or today if not on "economy 7" or whatever its called now and measure the actual tap temperature when it cuts out. How far above the bottom of the cylinder coil is the cylinder coil stat located?, if the circulation through the coil is lowish then there could be a dT of 15C or more between the upper yliner temperature and the bottom. My (PT1000) coil probe is located ~ 1/4 way up the coil bottom and there is ~ 10C dT between the tap temp and the probe temp, tap temp is ~ 68/70C with a SP temp of 60C at the end of the reheat period.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Indirect (Boiler Fed) Megaflo Doesn't Stop Heating" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
techweb,
Last reply from
techweb,
Replies
38
Views
3,106
Back
Top