Also system pressure loss (PRV leaking). Been twice before to recharge PV. Are the two issues linked or do we have two separate problems? I suspect div valve passing when DHW on preheat. Can anyone tell me which seal will need replacing?
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
:iagree: however if the phex is restricted you'll get the same symptoms! 🙂
Regards re-charging, on these bad boys the diaphragm on the expansion vessel can perish with all that heat and flow kicking about in it! Weird set up!
How do you recharge the PV? May be a daft question but not all folk are made aware of what it is they're doing in my experience and tend to close off the system when re-pressurising! 🙂
The water must be passing through the diverter valve dude, it's the only way rads should get hot on hot water/pre heat mode.
I drain the boiler by opening the drain, leaving it open while connecting my foot pump to the Schrader valve. I pump it up to about 1 bar and leave it for a few minutes to check there is no drop, close the drain then refill the system pressure. leave the foot pump attached to check the vessel pressure matches the system pressure before removing the foot pump.
So its a dv valve service kit including the plunger?
That's right, I seem to remember that the preheat uses the Expansion vessel, not sure of the set up but it would be the first port of call. There's water loss from prv would indicate a common denominator there:iagree: however if the phex is restricted you'll get the same symptoms! 🙂
Regards re-charging, on these bad boys the diaphragm on the expansion vessel can perish with all that heat and flow kicking about in it! Weird set up!
How do you recharge the PV? May be a daft question but not all folk are made aware of what it is they're doing in my experience and tend to close off the system when re-pressurising! 🙂
Did you clean out or replace the PRV when you sorted the expansion vessel? There could be a bit of sludge on the seating causing it to pass.
With regards to the radiators heating with the pre-heat, you can just replace the one section of the diverter valve, pretty easy to change.