more likely the gas valve setting is too low, needs to be 9.1 +/- .5%, min setting 8.6%, but they dont like running this low really. Only adjust gas valve with boiler running at min rate, then check at max rate for correct set up. follow the manual instructions for how to do it.
all boilers are preset but dependent on factors such as gas supply rate etc etc some adjustment is normally required to set them up to run at their best, or am I the one of the few that bothers to do this?
Well now we have the co test on commission then we should all be doing it...
Pretty sure WB instruct you to call the service line if adjustment is required on commission.
so another reason to avoid that make 🙂
So do intergas!
What could be the consequences of a poorly (outside of the min/max MI's) set up gas valve when adjusting the co2 air/gas?
Would the co ppm rocket? Boiler severely bang on ignition?
Fitted an inter gas today won't be bothering again
The flue turret pushes in, twist and locked in place, not seen any self tappers for the rest of the flue. The pump head is easy to change the grommets in the casing line up with Allen key