Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

You can normally find the gas rate of an appliance in the manufacturers instructions.

Failing that you can work it out off the Gross heat input whether that be in Btu's/hr or Kw/hr.

If you don't have manufacturers instructions they will be online or there may be a visible data badge on the appliance.

I use a calculation from my head but it is round the houses and one I have used since God knows when. It is accurate but I dare say there are more modern ways even if they do get you to the same answer.

If you google Kw to M3/hr gas, there are a few dotted about that will work.
I have used the 100,000 BTUS IS 100 cu ft since i Started and to convert 1 kw is a 1000 BTUS, it’s simple and pretty accurate which would make 64 kwatt is 640 cu ft
 
there is ~ 0.293 kwh in a cu ft gas or ~10.35 kwh in a cu meter
64 kwh = 64/0.293 or 218 cu ft . (6 cu meters)
there are 3412 btus in a kw.
 
Last edited:
  • Like
Reactions: Gasmk1
1 kw is 3412 BTUS as pointed out below I wasn’t fully awake when I wrote this
Mine goes like this, Kw x 3412 = Btu's /1040 (1037 at the mo calorific value of one cubic foot) = Ft3 /35.32 (near enough) = M3
Or My quickest method is Kw / 10.77 = M3 (really rough but good enough for small stuff).
 
Just read the full thread and the requirement is for 2 x 30 kw boilers, so to be on the safe side assume boiler efficiencies of 85% the requirement is 60/0.9 or 67 kw net, assuming "wet gas" loss of 10% then requirement is for 67/0.9 or 75 kw gross. Don't know what the average gross CV of UK gas is but (I don't have gas) the last bill I saw (here) showed 11 kwh/M3 so meter requirement is, 75/11 or 6.8M3.
There is probably a published regional gas gross CV for the UK?.
 
Probably OK so? if overall boiler efficiency is 85% (gross) then requirement is 6.6 M3.
 
That Imperial meter is badged as 565 cuft/hr.
That's 15.999 cu mtr /hr so under 16 as above posts.

When you contact engineers for quotes mention the meter is an Imperial U16, save them wasting yours and their time coming out to refuse to touch it.
And as above also test their knowledge and confidence.



It's be interesting to hear of a Smart Meter fitters reaction to the meter.

Smart meter fitter here. I knew from the first post it would be a imperial u16 lp meter. That's a walk away for me personally, too big for my spanner ;D.

Very surprised that the op's gas engineer wouldnt know that or be able to provide a new boiler for the op. Definitely get some more quotes and avoid the first lot.

Funny how people think they only have tiny 5 bed houses with 17! rads. I very much only find those meters in big houses. When I roll up on mansions like that my first thought is usually U16/3phase!
 