kirkgas
From IGE UP1B
5.4 NEW EXTENSIONS/ALTERATIONS TO EXISTING INSTALLATIONS
Before commencing the new work, the existing installation shall be tightness
tested in accordance with clause 5.3.2 and any permissible pressure drop over
the 2 minute test period noted (see also Sub-Section 4.2).
Upon completion of the work to the existing system, the tightness test shall be
repeated and the pressure loss after the 2 minute test period shall be no greater
than that previously measured and there shall be no smell of gas.
This is how it should be done.