ideal logic combi losing pressure daily. Initially i thought it was a leak on the system so all the pipework was checked and no leaks found
The flow and return were isolated overnight with no demand and there was a pressure drop. I disconnected the condensate pipe and put a bucket under it but no leak.
I did the check a second night but it didn't drop.
i thought i must have missed something so i have isolated the flow and return again and the pressure has dropped within 30 minutes by around 0.5bar.

Has anyone come across this before ?

The boiler is under warranty but i dont want ideal to come out and say its nothing to do with the boiler.
 
Get ideal out. Tell them.you have isolated the system pipework and pressure has still dropped.
 
Get them out on a warranty call, could have a pin hole in EX , but don't mess around with boiler if still under warranty
 