It seems that there is a fair bit of it about and its on the increase as the colder weather creeps on.
Typically,we would like to see a WP of around 19-22mb at the meter outlet but what happens when we dont get it?
TOO HIGH ? Well this is likely to be due to a faulty or maladjusted regulator. There are "replace on find" instructions on certain types of domestic regulator,most commonly,the Donkin 225/2 regulator. The reason? It has been found that the plastic valve can sometimes shear off due to fatigue and allow service pressure through to the installation.
TOO LOW ? Again it could be caused by a faulty or maladjusted regulator.
It may well be that the regulator is working ok but that the network can simply not deliver the pressure that we would aspire to.
It is now becoming accepted practice for distribution networks to manage the network pressures toward the lower end of the spectrum.
This can lead to lower pressures at the extremities of the network and in higher demand areas especially at peak demand times.
This is exacerbated by increased demand on existing networks due to upgrading of appliances. For example, a typical road will have a gas main of a particular size. A couple of decades ago it may have serviced a street full of domestic boilers of maybe 75,000 Btu input. Fast forward to today and everyone has 30Kw plus combis and you can see that during peak time demand,there may be reduced pressured and a certain amount of sharing of available gas.
Most domestic PE services that have been renewed will have been replaced with smooth bore 20mm PE. Many will also have been replaced using an insertion technique in which corrugated PE service is inserted inside the old steel SP.
So the issue becomes..is the low pressure consistently low or is it a peak demand issue?
Also..how do we measure it? I would suggest that the WP should be measured at the meter outlet with a combi boiler delivering hot water at the point where it is run from cold..i.e not modulating.
If it is found that it is simply a network issue,and that pressures are not excessively low...then the ESP will be likely to leave as found.
District regulators respond to demand and a measured low pressure on one day may well be found to be acceptable the next day.
Of course as far as the ESP is concerned,they only want to know about meter OL dynamic pressures.
Are you seeing increased low pressure reports?
Typically,we would like to see a WP of around 19-22mb at the meter outlet but what happens when we dont get it?
TOO HIGH ? Well this is likely to be due to a faulty or maladjusted regulator. There are "replace on find" instructions on certain types of domestic regulator,most commonly,the Donkin 225/2 regulator. The reason? It has been found that the plastic valve can sometimes shear off due to fatigue and allow service pressure through to the installation.
TOO LOW ? Again it could be caused by a faulty or maladjusted regulator.
It may well be that the regulator is working ok but that the network can simply not deliver the pressure that we would aspire to.
It is now becoming accepted practice for distribution networks to manage the network pressures toward the lower end of the spectrum.
This can lead to lower pressures at the extremities of the network and in higher demand areas especially at peak demand times.
This is exacerbated by increased demand on existing networks due to upgrading of appliances. For example, a typical road will have a gas main of a particular size. A couple of decades ago it may have serviced a street full of domestic boilers of maybe 75,000 Btu input. Fast forward to today and everyone has 30Kw plus combis and you can see that during peak time demand,there may be reduced pressured and a certain amount of sharing of available gas.
Most domestic PE services that have been renewed will have been replaced with smooth bore 20mm PE. Many will also have been replaced using an insertion technique in which corrugated PE service is inserted inside the old steel SP.
So the issue becomes..is the low pressure consistently low or is it a peak demand issue?
Also..how do we measure it? I would suggest that the WP should be measured at the meter outlet with a combi boiler delivering hot water at the point where it is run from cold..i.e not modulating.
If it is found that it is simply a network issue,and that pressures are not excessively low...then the ESP will be likely to leave as found.
District regulators respond to demand and a measured low pressure on one day may well be found to be acceptable the next day.
Of course as far as the ESP is concerned,they only want to know about meter OL dynamic pressures.
Are you seeing increased low pressure reports?