Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

View the thread, titled "magnaclean fitting" which is posted in UK Plumbers Forums on UK Plumbers Forums.

Status
Not open for further replies.
B

bilbomug

hi just bought a magnaclean and wondered if i could fit it above the boiler as in the picture
[DLMURL]http://img.villagephotos.com/p/2007-4/1252920/1.jpg[/DLMURL]

thanks
1.jpg
 
Last edited by a moderator:
Theoretically it should be OK as the heat of the unit will be largely governed by the temperature of the water inside it. I am going to do exactly this when I fit a new boiler tomorrow but I would think a little more carefully about doing it with an older boiler where the case can get quite warm. If your boiler is a potterton netaheat which is what the diagram looks like then I would want a minimum of 6-8 inches between the bottom of the magnaclean and the top of the boiler.
 
Last edited by a moderator:
Status
Not open for further replies.

Official Sponsors of Plumbers Talk

Reply to the thread, titled "magnaclean fitting" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Weekly or Monthly Email Digest

Back
Top