magnaclean fitting

View the thread, titled "magnaclean fitting" which is posted in UK Plumbers Forums on UK Plumbers Forums.

B

bilbomug

hi just bought a magnaclean and wondered if i could fit it above the boiler as in the picture
[DLMURL]http://img.villagephotos.com/p/2007-4/1252920/1.jpg[/DLMURL]

thanks
1.jpg
 
Last edited by a moderator:
Theoretically it should be OK as the heat of the unit will be largely governed by the temperature of the water inside it. I am going to do exactly this when I fit a new boiler tomorrow but I would think a little more carefully about doing it with an older boiler where the case can get quite warm. If your boiler is a potterton netaheat which is what the diagram looks like then I would want a minimum of 6-8 inches between the bottom of the magnaclean and the top of the boiler.
 