Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

ShaunCorbs

Super Moderator
Staff member
S. Mod
Plumber
Gas Engineer
Subscribed
May 23, 2015
35,144
1
14,996
113
North Wales (so hide all your sheep) :D
Member Type
Heating Engineer (Has GSR)
any done much with these as got two in series in a pub

readings im having doubts about

propane (lpg)

o2: 11.3%
co2: 6.87
Co: 0ppm
Ratio: 0.0000
eff: 88.6%
Ex Air 117%
Draught: -0.260

manual doesnt list any spec regarding readings

ex air im sure is too high

am i missing something
 
  • Like
Reactions: 1 person
CO2 looks low
O2 looks high
Did you gas rate it and check WP at appliance and Meter Shaun ?
is that with both running or one ?
 
  • Like
Reactions: 1 person
CO2 looks low
O2 looks high
Did you gas rate it and check WP at appliance and Meter Shaun ?
is that with both running or one ?

thinks its generally o2 too high thats bringing all the other readings down

lpg so no meter 34 working at appliance and 35 meter

but burner pressure is bob on

and singe (each got different flues) but there bot the same
 
If BP is around 32mb Max, it sounds right. I don't know reading for that boiler, I just know Vaillant is higher than that.

I know a man who will know. If I can get hold of him i'll ask and let you know !
 
If BP is around 32mb Max, it sounds right. I don't know reading for that boiler, I just know Vaillant is higher than that.

I know a man who will know. If I can get hold of him i'll ask and let you know !
 
If BP is around 32mb Max, it sounds right. I don't know reading for that boiler, I just know Vaillant is higher than that.

I know a man who will know. If I can get hold of him i'll ask and let you know !

thanks mate

nothing is listed other than bp in the mis

it started to **** me off

min and max rate only adjust bp which which fga end doesnt change much

tbh dont rate them much

going back next tues, any help with be appreciated
 

Official Sponsors of Plumbers Talk

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.