Hi

Can anyone suggest a simple guide book or web site describing how to test boiler components with a multimeter.

I recently checked a ferroli boiler when the fan was not proving,i called there tec detp and they suggested i tested the fans resistance which should have been 76 ohms.

They said to take of the blue and brown lead from the fan set my meter at 200 ohms and put one tip of the probes on each fan spade.

The reading should have been 76ohms yet it read 1 . basicaly nothing so the fan motor they said was no good,yet after opening the board cover up and checking connections i fired up the boiler and the fan worked dispelling the zero reading.
 
I went on a £50 one day boiler course at Worcester and was taught this then received a few really helpful hand outs.

I appreciate this won't help you tomorrow but could be worth looking into for the future.
 
i did the mr combi (well worth it) i also did the Vokera fault finding course (its free) and that one was just as good,
 
if your meter is reading 1 it may not on the right scale, and the fact the fan worked would suggest it either wasn't on the right scale or a cheap and nasty multimeter.
auto-ranging multimeters don't cost a lot and are good if you're not sure what your expected readings should be.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Multimeter testing" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
gregg1908,
Last reply from
pmac10,
Replies
7
Views
5,751
Back
Top