ahh didn't know its the same motor that runs the pump, still the cap value is so low it must be the run cap. single phase induction motors need a cap, some have a start cap and a run cap, some just a run cap.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Thanks. Im going to check to see if air getting in somewhere else, and clean band. Tell me more about the air diffuser. There definitely was not one there. How much difference does it make.? Is it something i can make without or do i need to make one up..washer.. what sort of diamiter . Would one work from another burner. .?I find the air settings on the aluminium band very sensitive to adjust. Like Best says they collect dust and fluff, make sure that's cleaned off. Could air be entering elsewhere?
There should be an air diffuser around the nozzle.
The plastic bit, no 17, locating block... No not replaced this. What is it for? I did not access through bank plate.Is the plastic bit replaced near the oil pipe to nozzle?
No. 17 on diagram.
The plastic bit, no 17, locating block... No not replaced this. What is it for? I did not access through bank plate.
Did you document it was unsafe to use?What is the advice around switching off unsafe boiler. I was taught that with oil we have no legal right to disconnect boiler. but if pumping out co @ 800ppm... Surely.. I told client on Friday boiler not safe and do not switch on, 3 times I told him. Could not believe when he said he had it on. Luckily it locked out...
What is the advice around switching off unsafe boiler. I was taught that with oil we have no legal right to disconnect boiler. but if pumping out co @ 800ppm... Surely.. I told client on Friday boiler not safe and do not switch on, 3 times I told him. Could not believe when he said he had it on. Luckily it locked out...
Ill keep that in mind. Ill take solenoid with me. For better piece of mind.I turn switches off and sometimes remove the solenoid to prevent burner firing.
Fuse out and oil off for extra safety.
Can’t trust customers or friends they bring later to interfere. Or children obviously can be at switches.
Update on boiler. Got there this am with new capacitor. On arrival noticed lock out on..Odd considering I had switched off at wall and at boiler and told client not to use boiler.. Different story..
Re-cleaned the now oil wet combustion chamber..*?@*%
Removed burner and removed fan and cleaned loosened air band and cleaned. Found small stone jammed in back of band preventing it closing fully. So when I thought I had closed air band there was actually gap at the back. TOO much air... So with that sorted . I replaced nozzle thanks to Kris's Myson performance data sheet, and set pressure. Done smoke test at low air and adjusted down to 2 smoke. Then fine tuned with FGA. Ended with 11.2 co2, 37% excess air, flue temp 277 C, 70 co ppm. any more air to bring co2 down a bit then co ppm rises. Not sure what the recommended co2 is for that boiler.
Anyway happier with that. All that headache from a 2mm stone..
Must say the air band is very fine movements to tune in. I ended up at just under 1 on the settings.