Is it ok to have more than one bypass valve on a system? Planning an UFH system (heat source supplied by air-water heat pump) with 2 manifolds, each with 6 circuits. Each manifold has its own motorized isolation valve connected to a room thermostat controller. Obviously the system needs a bypass in case both motorized valves are closed...however the heat pump specifies a minimum system pipe volume of 20 litres when all valves are closed...I've calculated each manifold leg has around 10 litres, so if there is only one bypass on one manifold it wouldn't be enough (since water would only flow through the one manifold with the bypass)... Any issue with installing a bypass on each manifold?? So two bypass valves? That way when all isolation valves close the system still has 20Ltrs