Dear all,


I’d be most grateful for your thoughts and advice.

I am a self-builder converting anagricultural shed to a small studio-type house. Its near Sevenoaks in Kent inthe middle of an orchard. I started it four years ago and am still nowhere nearcomplete - I am learning the hard way!

At the outset, Southern Gas Networks installeda service on the site which remains unused. They terminated their supply with ashut off valve in a meter box I had fitted in a garage on the site.

This is a straight 28m run away from thehouse. A further 2-3m should be allowed for entry to the house and connectionto a Worscester Bosch combi (24kW) and a gas hob (9kW).

The trench for the pipe run has already been dug


British Gas were due to fit a U6 meteryesterday whereupon I would have had the gas supply run on to the house.However I put this on hold following a telephone call with them in which theysuggested I take further advice before committing to it. This was on the basisthat they install meters free of charge but upgrade them if needs be atconsiderable charge!

I think their concern was that a U6 metermight not be large enough to provide the appliances with sufficient gas giventhe likely pressure drop over 30m.

Three questions arise from this upon whichI have been given completely contradictory answers, mostly, I must confess, bypub experts and Google!

I’m hoping somebody here can provide some clarity as follows:




  1. Is a U6 meter man enough tosupply 24kW + 9kW of appliances?
  2. What diameter yellow MDPE pipeshould be specified given a run of about 30m after the meter?

  3. How would the supply best bebrought into the house? Note that the construction is a timber frame sitting ona single skin, brick plinth wall with a solid floor. I have provided a100/110mm duct through the foundations and up through the floor to run all ofthe services from underground though I recognize now that this might not be appropriate for gas.

Once again, many thanks for reading thisand for any thoughts you may have. Needless to say, if any of you are local andcan issue a Gas Safe Certificate, there is a job here for you!

Best regards,


Jonathan
 
110 is a bit excessive as only need 32 mm sleeve . It would require 28 mm copper for defonate and the meter is large enough but we would need to know distance the hob n boiler is from the meter to ascertain how far the 28mm goes. Chances are 28mm would have to go to the first tee piece.
Best you get a gassafe registered engineer into measure up and check.
Welcome to the forum.
 
Kris, he says the 110mm is for all the services (I assume gas, water, cable tv and electricity, to name a few.
But as you say, better the OP gets someone to have a look
 
The gas meter is capable of providing the likely demand. The gas installation pipe will have to be sized according to the pressure drop over the run, which can be calculated by the gas safe registered engineer. The gas installation pipe must not be ducted under foundations. You can bring it up on the outside wall and then pass through above ground fitting an emergency control valve at point of entry. Hope this helps in your decision.
 
1. Plenty big enough
2. 32mm PE
3. Not up through that duct you have fitted. Its not allowed for pe to enter below a building in that way and the other way is specialised.

Apart from running the PE in a track, this is not a diy job. Any suitably qualified gas registered engineed "should" be able to keep you right.
Btw you are very near the limit for pressure drop and what can legally be worked upon with a domestic ticket.
 
Thanks to everybody who has replied to mypost.

I am reassured by what everyone says aboutthe G6 since a larger meter wouldn’t fit the meterbox I have painstakinglybuilt into a garage wall.

I will specify 32mm PE for the 30m run tothe boiler.

I provided a below ground entry for all ofthe services to be run through and Building control didn’t baulk when I pointedthis out to them. However I can’t push 25mm blue PE through the duct because ofa small radius 90 deg bend in it so would never get 32mm through even if itwere allowed! As I said, I am learning the hard way.

I will need a GSR installer to fit an aboveground entry for gas and to make the connection to the meter.

This will doubtless take time to arrange –you guys are always busy - but that’s not the problem. It’s not a problem thatI can’t have a hot bath in there either though I look forward to the day..

The problem is that I need to backfill about8m of the 28m trench thats been dug as soon as possible. This is because it’s completelyobstructing access to the building which is causing me all sorts of unrelatedheadaches. The trench is also starting to collapse.

So, would it be permissible for unqualifiedme to simply lay the 32mm PE pipe across the area I need to backfill, and then backfillleaving the ends free for the GSR installer to make the connection at each end? Or would I then find nobody prepared todo this?

Be interested in your thoughts on this. Also, what is meat by running PE in a track?


As a side, my recent experience might amusesome of you:


  • SGN will not do the pipeworkbecause it is after the meter
  • The BG meter boys will not fitthe pipework also because the run would be more than 5m.
  • The BG boiler installation boyswill not quote for fitting the boiler because there is currently no gas supplyto the building and they will not provide it.

It’s a mad world!

 
As an engineer, I would be looking at depth of cover and infill material. but get a gas safe registered fitter to check it over.
 
You need at least 450mm deep ' preferably on a layer of sand and cover it with a layer of sand then put a marker tape gas.jpgon top around 150mm above. Get a GSR to have a look before you backfill.

Terminate the PE at the house wall onto steel or copper and fit an AECV (an emergency control valve)
Run a suitably protected 1" mi (steel) pipe in your floor screed to your appliances (you can reduce it for the hob but bigger is better at very little extra cost).

Steer away from the gas board for your boiler.
A local GSR engineer will do as good a job much cheaper.
 
I cant find any GSR engineer willing (or perhaps able?) to work with yellow MDPE! I understand they need to use specialist fittings at each end.

Could somebody please give me a steer in the right direction?
 