The standing pressure at the outlet is regulated by the meter governor.Hi Guys,
Thanks to all who have commented so far!
Today BG fitted a shiny new U6 gas meter to the service provided by SGN.Actually, it's a reconditioned one but it looks very nice nonetheless.
Standing pressure at the meter was 23.5mbar.
I took the opportunity to measure the run of SGN’s service pipe which is nowburied. It's longer than I thought. Effective length is actually 30m and it's32mm yellow PE.
The difficulty remains what size pipe to specify to connect the meter tothe house which is a further 30m away (allowing for upstands andbends at each end). The supply will feed a 24kW WB combi and a 9kW gashob.
My instinct is to have it run in 63mm yellow PE despite it being five timesmore expensive than 32mm. My layman's logic is that if this doesn't provideenough gas flow at the house, then it will be down to SGN to upgrade their 32mmservice. Or am I being naiive in believing this?!
Also, this assumes there is a way of checking the gas flow rate withoutany of the appliances being fitted. Am I correct in believing that there is?
As ever, your comments and advice would be much appreciated. Having made somany costly mistakes elsewhere on the build, I am determined to getthis aspect right first time!
Cheers, Jonathan
30m of 32mm pipe has a volume of 0.048m3 plus meter plus other pipework. Probably still below 1m3 volume and less than 35mm so UP/1/B domestic test ok.
I told you the sizes in post 11 and 14.
I didn't just have a guess at these sizes.
Sorry guys, I have read all of your postsand have tried to digest all you have said.
What prompted my last post and what’s stillbugging me is that I realize now that the supply to the house from the gas mainin the street will actually be 60m.
The meter is half way along and I can’t doanything about SGN’s supply to it which is 32mm. It’s buried with all the otherservices and I’m sure that upgrading it now would cost SGN - or more likely me -thousands. So that isn’t going to happen.
With the benefit of hindsight, I’d have hadthe meter fitted nearer to the house as anz suggested, but the garage seemed theobvious place to put it at the time. I didn’t want a gas meter in the house or onein the ground outside.
So, for ermintrude and tamz, given thelength of the service pipe, do you still think that 32mm PE would suffice?
My worry is that if 32mm doesn’t work, SGNwill blame me when I would rather blame them for not providing an adequateservice!
Thanks again to all for the feedback
Jonathan