The other day i went along to help a guy who was having problems with a Worcs GS 40CDI which he had just installed.
The problem was that at the inlet test point on the GV,he was getting 7mb WP when the boiler was full on in engineering mode.
I set up guages on the ecv outlet and the meter outlet. The metter sounded like a bag of spanners and was of a make known to be problematic.
SP at SVC was around 25mb. With the clanky meter the WP at the SP was around 21mb and the WP at meter outlet was about 18
I stuck a new non clanky meter in and the reading on the outlet was now 20mb and at the boiler..it had risen to 10mb.
There was only the boiler fitted in the building on a run of about 15m of 28 tubing.
Blew it and no apparent obstruction.
Im thinking that there was an issue/possible obstruction of the test point on the Worcs GV...I left him to it..